What is my service entrance rated for?

It is an underground entrance with two 1/0 hot leads and a #2 neutral. The charts I have seen read the 1/0 is rated 175 amps but the #2 is only 125 amps. So with the neutral being smaller does that mean the entrance is only rated for 125 amps?

skeeter
 
  #2  
Old 01-12-18, 11:20 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,469
Received 1,420 Votes on 1,313 Posts
When discussing poco service cables things are a little different. They don't follow the NEC code the same as we do.

However, cables run thru a conduit are limited in ampacity.
More than likely your service cables are aluminum. 1/0 is 135A max.
 
  #3  
Old 01-12-18, 11:32 AM
S
Member
Thread Starter
Join Date: Jul 2009
Location: United States
Posts: 238
Received 0 Votes on 0 Posts
Sorry accidently posted on wrong forum. Can a moderator move it to Electrical AC-DC forum?
 
  #4  
Old 01-12-18, 11:36 AM
S
Member
Thread Starter
Join Date: Jul 2009
Location: United States
Posts: 238
Received 0 Votes on 0 Posts
PJmax, you are correct. I did not catch that they are aluminum cables. So the amperage capacity of the panel would be 125amps?

skeeter
 
  #5  
Old 01-12-18, 11:50 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,469
Received 1,420 Votes on 1,313 Posts
Correct and thread moved to electrical.
 
  #6  
Old 01-12-18, 11:59 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,250
Received 112 Votes on 97 Posts
The neutral is allowed to be sized smaller than the ungrounded hot conductors. The service size is not based on the neutral size.
 
 