Long run / breaker size ?

In one of our cow lots we have a tractor shed, it has a 10/2 underground wire ran 575 ft. To main breaker box,
it was buried approx 24 deep, and was to just supply power for a 90 watt 120 volt dipstick heater
According to the online calculator 10/2 wire at 575 ft, is good for 4 amps with 5% voltage drop.
now as I said the dip stick heater is only 90 watts at 120 volts.
my question is : what size breaker should I have at main box, and should at the end of run have a gfci outlet that the 90 watt dipstick heater be pluggd
Into
thank you for your time
​​​​
 
Sponsored Links
  #2  
Old 01-20-18, 02:31 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,546
Received 508 Votes on 478 Posts
Welcome to the forums.

You can use a 20A breaker. Technically the wire is rated for 30A but you cannot protect a regular 120v service receptacle with anything over 20A.
 
  #3  
Old 01-20-18, 11:47 PM
Member
Thread Starter
Join Date: Jan 2018
Posts: 2
Received 0 Votes on 0 Posts
Thank you pjmax for your input, now should I also have the outlet as a gfci ?
 
  #4  
Old 01-20-18, 11:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,546
Received 508 Votes on 478 Posts
A GFI receptacle would be a very good idea.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: