Switch Off / Low Voltage on One Outlet - Switch On / All OK

Just moved into a 45 year old house... There is a light switch in the basement that controls multiple receptacles.. or well, seems to have an impact on multiple receptacles.

Anyway.. how this started... I went to plug in a device and noticed it was only barely powering on.

I ended up tested each outlet on a few of the receptacles. One outlet on each read 52 volts... the other outlet on each, measured 120 volts. These are standard, two 3-prong outlet receptacles..

I noticed a switch off nearby -- new house (to me), unclear what it did... turned the switch on, now everything reads 120 volts.

What could I be dealing with here? Could this simply be a bad switch, or something worse?
 
Sponsored Links
  #2  
Old 02-02-18, 04:42 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Move any backstabs at the problem receptacle to the screws and redo the the other connections. Redo any wire nuts. Repeat at the good receptacle.
 
  #3  
Old 02-02-18, 04:47 PM
M
Member
Thread Starter
Join Date: Feb 2018
Location: US
Posts: 17
Received 0 Votes on 0 Posts
I'm not sure there are good receptacles.. only 1 seemingly good outlet per receptacle.
 
  #4  
Old 02-02-18, 04:51 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
What you are calling an "outlet" is a receptacle. Receptacle is where you plug something in. Outlets are any where power is tapped including lights and switches.
 
  #5  
Old 02-02-18, 04:54 PM
M
Member
Thread Starter
Join Date: Feb 2018
Location: US
Posts: 17
Received 0 Votes on 0 Posts
Ok, this gets weirder.. I found a second light switch on the other side of the room that was OFF.. Here are my findings... keep in mind, multiple receptacles

Both Switches OFF
Plug 1 (52v)
Plug 2 (120v)

Either Switch On
Plug 1 (120v)
Plug 2 (120v)

Both Switches ON
Plug 1 (45v)
Plug 2 (120v)
 
  #6  
Old 02-02-18, 06:04 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Are the switches 3-way switches? (No on/off markingings)
 
  #7  
Old 02-02-18, 06:15 PM
M
Member
Thread Starter
Join Date: Feb 2018
Location: US
Posts: 17
Received 0 Votes on 0 Posts
No on/off markings on the switches..
 
  #8  
Old 02-02-18, 10:43 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
So you have a set of 3-way switches. Tell us all the wires and connections in each switch box including what wire on the common terminal (usually dark gray, the odd colored screw).
 
  #9  
Old 02-03-18, 01:55 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,142
Received 83 Votes on 71 Posts
Were you having an issue or just measuring voltage?
 
  #10  
Old 02-03-18, 07:22 AM
M
Member
Thread Starter
Join Date: Feb 2018
Location: US
Posts: 17
Received 0 Votes on 0 Posts
The issue was that.. I got a space heater in the mail, wanted to plug it in to give it a quick test.

Heater would not come on.. but I noticed the power light came up, but very dim.... after that I started measuring voltages, which came up low... then I started playing with the switches and doing more measuring.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: