Gremlins running amok in my load centers.....Need help!
I am in the process of remodeling a house I bought 6 years ago which is located in Kerr County Texas ergo no codes applicable to this area. The electrical system in the house is down right scary so I am completely re-wiring the house. There is a main panel and two sub-panels. The main panel is in good shape and only about 10 years old. I have replaced one sub-panel (the First Panel,60 amp)which serves the water heater, master bath, master bedroom, and a second bedroom and have had no problems up until now.
I am now replacing the second panel and in doing so I decided to disconnect the ground wire from the first panel (The ground wire was cut too short so they pigtailed a section to extend it. This is where I disconnected it). In doing so, I got zapped from the ground wire. Using a multimeter, I checked the voltages on the legs. For purposes of my discussion I will use the following nomenclature: Line 1 - hot leg 1, Line 2 - hot leg 2, G - ground wire from first panel, E - Earth. With the ground DISCONNETED I have the following voltages: Line 1 to Line 2 - 245V, Line 1 to G - 246V, Line 2 to G - 5(Five)V, G to E - 120V
Line 1 to E - 120V, Line 2 to E - 120V and G to E 120V. I have 245V across Line 1 o Line 2 at the terminations in the first panel but none of the circuits in the first panel work.
Reconnecting the ground wire back I get the expected readings Line 1 to Line 2 - 245V, Line 1 to G - 124V, Line 2 to G - 124V and the first panel circuits work.
Can anyone shed some light on to this dilemma? Any suggestions would be greatly appreciated.
I am now replacing the second panel and in doing so I decided to disconnect the ground wire from the first panel (The ground wire was cut too short so they pigtailed a section to extend it. This is where I disconnected it). In doing so, I got zapped from the ground wire. Using a multimeter, I checked the voltages on the legs. For purposes of my discussion I will use the following nomenclature: Line 1 - hot leg 1, Line 2 - hot leg 2, G - ground wire from first panel, E - Earth. With the ground DISCONNETED I have the following voltages: Line 1 to Line 2 - 245V, Line 1 to G - 246V, Line 2 to G - 5(Five)V, G to E - 120V
Line 1 to E - 120V, Line 2 to E - 120V and G to E 120V. I have 245V across Line 1 o Line 2 at the terminations in the first panel but none of the circuits in the first panel work.
Reconnecting the ground wire back I get the expected readings Line 1 to Line 2 - 245V, Line 1 to G - 124V, Line 2 to G - 124V and the first panel circuits work.
Can anyone shed some light on to this dilemma? Any suggestions would be greatly appreciated.
#2
Welcome to the forums.
We're going to need pictures.... How-to-insert-pictures
From what you are describing..... there is no neutral there. Only a combination ground/neutral which cannot be opened under power. Sub panels now are wired with four wires. Two hots, a neutral and a ground.
We're going to need pictures.... How-to-insert-pictures
From what you are describing..... there is no neutral there. Only a combination ground/neutral which cannot be opened under power. Sub panels now are wired with four wires. Two hots, a neutral and a ground.
#3
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,705
Received 273 Upvotes
on
230 Posts
As said you have no neutral. Subpanels should be updated with a 4 wire feeder. In the subpanel the grounds are bonded to the panel and will most likely require the addition of a ground bar kit. The neutrals will connect to existing bar but that bar needs to be isolated from the panel and grounds. Isolating the existing bar usually requires the removal of a screw or strap that bonds the bar to the panel.
#4
Member
Thread Starter
Join Date: Feb 2018
Location: USA
Posts: 8
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Here is the photo of the main panel. I had the electric company out this AM to cut off the power for some other work I needed and I asked them about the situation. They confirmed your suspicions that the ground was being used as the neutral. So I am going to rewire both circuits in the panel to have independent neutrals.
Thanks to all for your guidance.
Best Regards.
Thanks to all for your guidance.
Best Regards.
Last edited by ray2047; 02-06-18 at 08:47 AM. Reason: Enlarge and rotate image
#5
The OP's post and description was at best confusing, but I believe he is using the term "Ground" when he should be saying "Neutral" and using the term "Earth" when he should be saying "Ground". If I have the post figured out correctly, I suspect that what he did was disconnect the Neutral under load and that would account for his getting zapped.
If "G" is really "Neutral" and the Neutral has been disconnected to the subpanel, which he said he did, this would be correct. If all the branch breakers in the subpanel were turned off then the reading would be 0 volts.
Line 1 to G - 246V
If "G" is really "Neutral" and the Neutral has been disconnected to the subpanel, which he said he did, this would be correct. If all the branch breakers in the subpanel were turned off then the reading would be 0 volts.
#7
I took G as being the equipment ground between panels
He has identified that he understands the problem and will be running four wire cables to his sub panels.