Adding a sub panel

Reply

  #1  
Old 02-06-18, 10:41 AM
M
Member
Thread Starter
Join Date: Feb 2018
Posts: 1
Received 0 Votes on 0 Posts
Adding a sub panel

I am working on a remodel and have to add a 100amp sub panel to the garage, it is a 165ft run from the main panel. I will be adding 2 in ground junction boxes because the run will exceed 360į in bends. I'm thinking of running 3 2/0 aluminium and #6 ground. Let me know what ur thoughts are on this
 
Sponsored Links
  #2  
Old 02-06-18, 12:12 PM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The ground needs to increase to #4 aluminum or #6 copper, but other than that the plan sounds OK. Burial depth for the conduit needs to be 18" to the top of the pipe.

Why so many bends?
 
  #3  
Old 02-06-18, 05:29 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,318
Received 45 Votes on 38 Posts
2/0 Al is a bit big for 100A. 1/0 is plenty and even #1 would be enough at 165ft providing you are not loading it to the max of 100A all the time.
 