New guy, need help with dead outlets

Reply

  #1  
Old 02-07-18, 12:43 PM
L
Member
Thread Starter
Join Date: Feb 2018
Location: United States
Posts: 2
Received 0 Votes on 0 Posts
New guy, need help with dead outlets

Sorry for new guy questions, couldn't find my issues in the previous threads. Four outlets are no longer functional. Checking the dead outlets I observed between Phase, Neutral and Ground; P-N low to 0 volts, P-G 120v or near it, N-G 120v or near it. Killing the power I observed Continuity between P-N with No Con. between the others.

The outlets on the same circuit that are working P-N 120v or near it, P-G 120v or near it, N-G 0v or near it. For Conitnuity I have Continunity between N-G and not the others.

Breaker seems to be operating correctly, have taken apart non functioning outlets no problems observed, One of the non functioning outlets is a GFCI. Last actvity on outlets before non function was workiing small 2hp compresor. Operation seemed fine and not till later noticed light in same circuit not working.

I need help in diagnosing possible issues, and advice on how to proceed with a solution.
 

Last edited by Larsonclan; 02-07-18 at 12:45 PM. Reason: Forgot to add more info
Sponsored Links
  #2  
Old 02-07-18, 12:59 PM
pugsl's Avatar
Forum Topic Moderator
Join Date: Mar 2008
Location: United States
Posts: 8,809
Received 50 Votes on 46 Posts
Look for a loose wire nut or connection in the last working outlet or the first dead outlet in circuit. If any back stabs in outlet move them to the screws.
 
  #3  
Old 02-07-18, 01:34 PM
L
Member
Thread Starter
Join Date: Feb 2018
Location: United States
Posts: 2
Received 0 Votes on 0 Posts
Does it sound like just a loose connection somewhere or do I have a N touching a P somewhere in the series
 
  #4  
Old 02-07-18, 05:57 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 56,394
Received 747 Votes on 702 Posts
No.... N is not touching P (or commonly known as hot)
You have an open neutral. You need to identify everything on the circuit. The problem will be at the last working device or the first dead one. If the problem is at a receptacle..... it could mean that the push-in wiring terminals were used and they get loose with age. Any pushed-in wiring should be moved to the side screw terminals.

If the problem is not at a receptacle.... it could be at s light or a switch box. In that case you'd be looking for a problem neutral (white) splice.
 
  #5  
Old 02-07-18, 06:34 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
N touching P (sic) is a dead short and pop goes the breaker.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: