How can a light bulb work with only hot wire and no neutral?
#1
Member
Thread Starter

I have an old circuit which has absolutely nothing but 1 light fixture with the pull string attached to it (so you pull light goes on, pull again, goes off). With the neutral disconnected from the bus bar. The light continues to work. How is this possible?
#2
The neutral you disconnected at the bus bar might not be for that circuit. Do you have a multi meter or electric tester to check the wires at the fixture. You could check to see if the neutral or ground wire is completing the circuit.
#3
If you are 100% sure that the neutral you disconnected is for the same circuit your light is on, it is possible something is wired wrong.
There may be a borrowed neutral from different circuit (which is wrong)
It may be part of multi wire branch circuit (MWBC). Is it on 2 pole breaker? Never turn this circuit on with neutral disconnected because it will introduce over 120V on some circuit and can fry what ever is on the circuit.
You may have neutral shorted to ground somewhere.
There may be a borrowed neutral from different circuit (which is wrong)
It may be part of multi wire branch circuit (MWBC). Is it on 2 pole breaker? Never turn this circuit on with neutral disconnected because it will introduce over 120V on some circuit and can fry what ever is on the circuit.
You may have neutral shorted to ground somewhere.
#4
Member
Thread Starter
If you are 100% sure that the neutral you disconnected is for the same circuit your light is on, it is possible something is wired wrong.
There may be a borrowed neutral from different circuit (which is wrong)
It may be part of multi wire branch circuit (MWBC). Is it on 2 pole breaker? Never turn this circuit on with neutral disconnected because it will introduce over 120V on some circuit and can fry what ever is on the circuit.
You may have neutral shorted to ground somewhere.
There may be a borrowed neutral from different circuit (which is wrong)
It may be part of multi wire branch circuit (MWBC). Is it on 2 pole breaker? Never turn this circuit on with neutral disconnected because it will introduce over 120V on some circuit and can fry what ever is on the circuit.
You may have neutral shorted to ground somewhere.
Basically this entire circuit can be thought of as a spare circuit. It was connected to something probably and they terminated it and wired up that light fixture. The light fixture is 2 feet away from the breaker box. So imagine there is a circuit breaker -> 3 feet of NMB -> light fixture. It's pretty simple. There is absolutely nothing else to it.
The light fixture has one of those pull strings so it has a switch built in. Can that explain why? I mean I'm just quite puzzled how this is possible and how there can be no explanation. I opened up the light fixture and I see black, white, and ground cables connect to the light fixture properly.
#6
Member
Thread Starter

#7

Does the bulb burn brighter or dimmer with the neutral disconnected?
It's possible you have a Multi-Wire Branch Circuit where two hots from different phases share a neutral.
If this is the case, when you disconnect the neutral at the panel, you create a 240 volt circuit (Hot leg to Hot leg).
If your breaker has two "trip handles" (above-and-below or side-by-side), do not disconnect the neutral before disconnecting both hots.
It's possible you have a Multi-Wire Branch Circuit where two hots from different phases share a neutral.
If this is the case, when you disconnect the neutral at the panel, you create a 240 volt circuit (Hot leg to Hot leg).
If your breaker has two "trip handles" (above-and-below or side-by-side), do not disconnect the neutral before disconnecting both hots.
#8
Member
Thread Starter
Does the bulb burn brighter or dimmer with the neutral disconnected?
It's possible you have a Multi-Wire Branch Circuit where two hots from different phases share a neutral.
If this is the case, when you disconnect the neutral at the panel, you create a 240 volt circuit (Hot leg to Hot leg).
If your breaker has two "trip handles" (above-and-below or side-by-side), do not disconnect the neutral before disconnecting both hots.
It's possible you have a Multi-Wire Branch Circuit where two hots from different phases share a neutral.
If this is the case, when you disconnect the neutral at the panel, you create a 240 volt circuit (Hot leg to Hot leg).
If your breaker has two "trip handles" (above-and-below or side-by-side), do not disconnect the neutral before disconnecting both hots.
#10
Is it an LED bulb or a standard incandescent? LED bulbs can light up from very small currents even when their hot line is off. This can happen sometimes when there is an electronic dimmer in the circuit and the LED sees a path through the electronics. I think you have a separate thread about what may be a surge protector on your main panel. That could possibly be a path for a very small current that might light an LED.
#11
Member
Join Date: Jul 2009
Location: Ca
Posts: 231
Received 0 Votes
on
0 Posts
Just a guess but perhaps the light fixture is grounding out to the box it is mounted to and completing the circuit through ground. If not mounted to a box then grounding through the fixture to the ground wire in the NM.