Do I need to use conduit?

If I run 2-2-2-4 wire to a subpanel in my garage do I need to run it through conduit? The wire would be run in a wall, across my attic, and then down to the panel in my garage.
 
  #2  
Old 03-24-18, 05:50 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Wire is a single conductor.By 2-2-2-4 did you mean four separate wires not cable? If so then yes it must be in conduit.
 
  #3  
Old 03-25-18, 07:00 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,705
Received 273 Upvotes on 230 Posts
If you are talking about 2-2-2-4 SER cable that has an overall outer sheathing no conduit is needed. If any part of the cable is subject to possible damage then that part needs to be sleeved in conduit.
 
 