Copper-clad aluminum wire splices.

Reply

  #1  
Old 03-27-18, 03:36 PM
L
Member
Thread Starter
Join Date: Nov 2015
Posts: 1,467
Received 70 Votes on 64 Posts
Copper-clad aluminum wire splices.

Most receptacles and switches I have seen are compatible with copper clad wires and as far as I know I can connect CCA wire to them without a issue.
However, I'm not sure about splices.
NEC 110.14 states
Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use.
I cannot seem to be able to find information on whether regular wire nuts are approved for copper to copper-clad aluminum. They only specify wire size, not type of wire.

Do I need to use special connector for splicing these with copper?
 
Sponsored Links
  #2  
Old 03-27-18, 03:49 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,631
Received 208 Votes on 185 Posts
That information will be found on the connectors manufactures website
 
  #3  
Old 03-27-18, 04:17 PM
L
Member
Thread Starter
Join Date: Nov 2015
Posts: 1,467
Received 70 Votes on 64 Posts
I looked up at Ideal website and it only states wire sizes and quantities. Doesn't mention wire type.

With UL listing, now it is even more confusing.

https://standardscatalog.ul.com/stan...tandard_486c_7

UL 486C states:
1.3 These requirements cover splicing wire connectors intended for:

a) Copper-to-copper;

b) Aluminum-to-aluminum;

c) Copper-clad aluminum-to-copper-clad aluminum;

d) Copper-to-aluminum or copper-clad aluminum and aluminum-to-copper-clad aluminum conductor combinations intended for intermixing of conductors and dry locations only; or

e) All of the above.

But, this would mean regular wire nut is allowed even for aluminum to copper as long as they are in dry locations..
 

Last edited by lambition; 03-27-18 at 06:37 PM.
  #4  
Old 03-27-18, 05:23 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,150
Received 87 Votes on 74 Posts
Regular wire nuts are for copper to copper only.
 
  #5  
Old 03-27-18, 05:30 PM
L
Member
Thread Starter
Join Date: Nov 2015
Posts: 1,467
Received 70 Votes on 64 Posts
Not a single manufacturer of wire nuts (at least major ones) mentioned copper clad aluminum.
Since the only concern (at least what I know of) of connection between copper clad and copper wire is different thermal expansion coefficient, perhaps a push-in connectors are the better choice?
 
  #6  
Old 03-27-18, 06:12 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,069
Received 1,109 Votes on 1,029 Posts
How many connections do you need to make ?
Push-in type devices have never been well suited to any type of aluminum wiring.
 
  #7  
Old 03-27-18, 06:17 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,631
Received 208 Votes on 185 Posts
Push in wire connectors would be a WORSE choice and are certainly not rated for copper clad aluminum. Something like this would be your best option: https://www.homedepot.com/p/AlumiCon...FRJqwQodC4oOgg

Or these: http://www.idealindustries.co.uk/ind...k=12702&fk=304

Or replace the wire/cable.
 
  #8  
Old 03-27-18, 06:22 PM
L
Member
Thread Starter
Join Date: Nov 2015
Posts: 1,467
Received 70 Votes on 64 Posts
I will make about 4 connections (3 per connection).
This is for installing recessed lights.

Dimmer switches I will be using states copper or copper-clad.
All information I'm finding about copper-clad aluminum suggests that it is just as good as copper wire and can be used in devices designed for copper only. However, I cannot find any information about copper to copper-clad splices other than NEC states that cannot be intermixed.
Also unable to find any connectors specifying copper-clad wire.
I'm pretty sure copper-clad to copper-clad will be find with regular wire nut. Not so sure about copper to copper-clad.


Push in wire connectors would be a WORSE choice and are certainly not rated for copper clad aluminum. Something like this would be your best option: https://www.homedepot.com/p/AlumiCon...FRJqwQodC4oOgg

Or these: http://www.idealindustries.co.uk/ind...k=12702&fk=304

Or replace the wire/cable.
While I'm sure AlumiConn will work fine, it also is not rated for copper-clad since it doesn't mention it at all.
Aluminum wire and copper-clad aluminum is very different type of wire.


NEC also states

Screwless pressure terminal connectors of the conductor push-in type are for use only with solid copper and copper-clad aluminum conductors.
The reason why I though push-in connectors many be a better option.
 

Last edited by lambition; 03-27-18 at 06:37 PM.
  #9  
Old 03-28-18, 09:33 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,651
Received 86 Votes on 76 Posts
I cannot seem to be able to find information on whether regular wire nuts are approved for copper to copper-clad aluminum.

I would treat copper clad aluminum wire as aluminum wire and use the AlumiConn connectors. If you use traditional wire nuts, the zinc plated spring will cut through the copper cladding into the aluminum and create the same old problem aluminum wire was always known for.
 
  #10  
Old 03-28-18, 05:34 PM
L
Member
Thread Starter
Join Date: Nov 2015
Posts: 1,467
Received 70 Votes on 64 Posts
Checking existing splices, I did not see any damage to the copper cladding with regular wire nuts. However, I have decided to use alumiconn for copper to copper-clad connections and regular wire nut for ground and copper-clad to copper-clad splices.

As for the switches, they do say it is for copper or copper clad, so I'm just connecting them directly. I haven't seen damage to the copper clad under screws either. Cladding is pretty thick.

I haven't found a single article about copper-clad causing problem, but did find article saying it is just as safe as copper. So, I guess they are good as long as no damage to the cladding occurs.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: