another grounding issue
something like this may have already been asked & answered. If it has, I apologize, but its pretty time-consuming to go back through all posts that has grounding in the title. This concerns the grounding of the main breaker panel. From what I've been able to determine, I have a ground at the meter or service entrance, a bare copper ground running through the outside wall conduit into the panel to a buss bar, and a ground wire that is bonded to the cold water supply. That's all I see. Is this enough, or should I put in a ground rod as well?
#2
At one time.... only the bond was required to the main water pipe.
You can add a ground rod. It gets connected to same place the bare ground is installed in the main panel. You can use solid or stranded green #8 THHN/THWN for a 100A service.
You can add a ground rod. It gets connected to same place the bare ground is installed in the main panel. You can use solid or stranded green #8 THHN/THWN for a 100A service.
#5
It sounds like your socket is where the rod was driven instead of the panel. Can you post a picture ?
Last edited by pcboss; 05-02-18 at 06:02 PM.
#6
Member
Thread Starter
Join Date: Apr 2018
Location: USA
Posts: 10
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Not of the socket, no. Its locked shut by the utility company. But I think there must be a rod in the ground just below the meter next to the exterior wall. There's what appears to be an old 6 ga. Bare copper wire running directly from the meter enclosure straight into the ground. Cable, phone, and ac compressor have been bonded onto this ground.