Wiring selection for sub panel

I have 100 amp main service coming into my garage and Id Like to place a 60 amp sub panel right next to it. Id rather not use conduit, so I was thinking of using SER cable but I wanted to double check the gauge and type (aluminum or copper). I was thinking of going with 6-6-6-6 copper SER cable. Would this be a safe choice? Or is there something more common that is used?
 
Sponsored Links
  #2  
Old 05-08-18, 07:09 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,997
Received 40 Votes on 35 Posts
Just use a conduit nipple between the boxes.

You will not find SER with a full size ground. It is not needed to be full size.
 
  #3  
Old 05-08-18, 07:27 AM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,256
Received 33 Votes on 27 Posts
Originally Posted by pcboss View Post
Just use a conduit nipple between the boxes.

You will not find SER with a full size ground. It is not needed to be full size.

????? 6-6-6-6 Cu SER is available. Sizes larger than #6 is when you see reduced size ground.
 
  #4  
Old 05-08-18, 08:24 AM
Member
Thread Starter
Join Date: Jun 2017
Posts: 38
Received 0 Votes on 0 Posts
I should rephrase about the main panel. It is mounted to a stud and recessed into drywall. So I was planning on mounting the sub panel the same way in the stud bay next it.
 
  #5  
Old 05-08-18, 08:58 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,997
Received 40 Votes on 35 Posts
You could mount the panel below the other one.

For 60 amps you could use 6-3 NM. It has a #10 ground. It is all that is required for a circuit up to 60 amps.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: