2 blown outlets

I have 2 outdoor receptacles with 3 prong outlets. I was doing work with an electric hedge trimmer and accidentally cut the extension cord. Now both that receptacle and the one in the back yard patio don't work. I have tried all the breakers. Could I have blown the outlets? Thanks for any help
 
  #2  
Old 05-18-18, 11:34 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,977
Received 194 Upvotes on 170 Posts
Look for a tripped gfi . It may be in the garsge, basement or bathroom .
 
  #3  
Old 05-18-18, 11:34 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 27,592
Received 2,144 Upvotes on 1,920 Posts
Even if your circuit breakers don't look tripped turn them completely off and then back on. If that doesn't work look for a GFCI somewhere that might have tripped.
 
  #4  
Old 05-19-18, 10:13 PM
S
Member
Thread Starter
Join Date: May 2018
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
I have switched all the breakers multiple times. The only gfi I have is in the bathroom and it didn't trip. I reset it anyway to be sure. Still no juice.
 
  #5  
Old 05-19-18, 11:10 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Often the GFCI is behind something that hasn't been moved in years.

If still no luck you need to open the boxes and look for failed connections. Do you have a multimeter or neon test light? (No a non contact tester won't work for serious testing.)
 
  #6  
Old 05-20-18, 04:35 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 27,592
Received 2,144 Upvotes on 1,920 Posts
Usually circuits are daisy chained with one outlet being connected to another and another. Once you are absolutely certain there are no hidden gfci you start checking outlets. I usually start with the dead ones. Remove the cover plate and pull the outlet out while still leaving its wires attached. Check all the wires for current. If none then move on to the next outlet. If you don't find power anywhere in the enclosure for our dead outlets then I move on to other nearby outlets that are hot. I'm looking for an outlet where power goes in and has wires going out but are not energized/hot.
 
  #7  
Old 05-20-18, 03:49 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 16,321
Received 38 Upvotes on 30 Posts
After moving into my current house I noticed the two small appliance branch circuits in the kitchen had only one GFCI receptacle. Neither of the two bathrooms had GFCI receptacles and the outside receptacle on the back porch did not have a GFCI receptacle.

My house was built in 1987 so the requirement for GFCI protection of these circuits was definitely in place. I had two GFCI circuit breakers in the panel and testing showed these to be on the two kitchen appliance circuits. That meant that the GFCI receptacle in the kitchen was redundant and had been installed by someone not knowing what they were doing. Turning off these two circuit breakers removed power from the kitchen (and dining room) receptacles but had no effect up[on the bathrooms or the outside receptacle. That told me that SOMEWHERE was located a GFCI receptacle OR that my home had some huge wiring mistakes.

I used a GFCI testing device in the front bathroom and it did trip something somewhere as I no longer had power at that receptacle. Testing the back bathroom and outside receptacle showed that these also had lost power. Now the search was on to find that hidden GFCI receptacle.

No other receptacle in the entire house was a GFCI type and that included the garage however I DID notice the lone receptacle in the garage (not counting the one for the door opener) had an adapter providing 6 places to plug in a cord. This adapter fully covered the face of the installed receptacle and when I pulled the adapter off there was the GFCI with the reset button tripped out. I reset it and the bathroom and outside receptacles again had power. Obviously the wiring went from the garage to the front bathroom to the back bathroom and then outside.

Not too long after I changed the receptacles in the bathrooms so that each had its own independent GFCI receptacle.
 
  #8  
Old 05-20-18, 04:04 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,816
Received 3,922 Upvotes on 3,518 Posts
Not too long after I changed the receptacles in the bathrooms so that each had its own independent GFCI receptacle.
An excellent idea. Saves hunting for a tripped one.

I work in a condo association that was wired with one GFI receptacle, usually in the upstairs bathroom, feeding three bathroom receptacles, garage receptacles, two outside receptacles and one in the basement. What a pain. Many customers have opted for multiple GFI receptacles.
 
 