vac difference between legs of service
Old 05-28-18, 10:42 AM
How much difference in voltage between the two legs of a service, seen while under load, would you suspect a loose neutral? How much would you say is normal?
note I am saying under load, I would suspect both sides should be within a volt not under load.
Old 05-28-18, 10:57 AM
Received 519 Votes on 489 Posts
Under no load...... the voltages should be almost the same.
Depending on the load.... I would say no more than a 10 volt difference.
A 240v load will not unbalance the legs.
A heavy 120v load can cause an imbalance.
The further you are from the utility transformer the greater the drop.
Old 05-28-18, 11:07 AM
pcboss's Avatar
Received 40 Votes on 35 Posts
Depending on the loads the voltage swing can be quite a bit.
Old 05-28-18, 11:36 AM
And is the push/pull effect normal?
for example a hair dryer might bring one leg DOWN 2 vac and the other side RAISES 2 vac.
Old 05-28-18, 11:40 AM
pcboss's Avatar
Correct. If one leg goes down by 30 volts the other leg goes up 30 volts.
Old 05-28-18, 05:08 PM
Received 42 Votes on 40 Posts
I would say that if the other leg goes up by more than five volts then you should assume you have a broken neutral problem.
If the leg you are using a lot of power on goes down by several volts and the other leg also goes down by a volt or two then you do not have a neutral problem.