I have a shed that is 10 feet from my house and the main power line connection-there are currently two separate wires running to the shed-I would like to get rid of these wires and switch to buried conduit but am unsure what type of wire to use-any advice?
Thanks
sbryant
 
  #2  
Old 05-28-18, 09:51 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,582
Received 13 Votes on 11 Posts
By two wires currently running to the shed do you really man wires or cables?

what type of wire to use-
Do you want just a single 120 volt 20 amp feed.
 
  #3  
Old 05-29-18, 05:54 AM
S
Member
Join Date: Mar 2013
Location: USA
Posts: 72
Received 0 Votes on 0 Posts
You can use THHN inside buried conduit. If you want to run a buried wire, it would need to be U.F, type. Either way, code calls for a fused or circuit breaker disconnect inside the shed. You can't just run to an outlet or switch. If you want 120/240V service to the shed, you need 4 wires..., 2 hot, 1 neutral and 1 ground.
 
  #4  
Old 05-29-18, 06:37 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,582
Received 13 Votes on 11 Posts
If you want to run a buried wire, it would need to be U.F, type.
UF is not wire it is a cable. Wire is a single conductor. Cable is to or more wires on a metaliic or a non metallic sheath such as UF.

Either way, code calls for a fused or circuit breaker disconnect inside the shed.
No. Per NEC a single 120 volt circuit* requires only a disconnect such as a light type switch, no fuse or breaker box needed.

* A multiwire feed which provides two 120 volt circuits can also be use with only a disconnect, either a pull out such as used for air conditioners or a two pole toggle switch.
 
  #5  
Old 05-29-18, 06:39 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,224
Received 105 Votes on 91 Posts
A simple toggle switch will work as a disconnect on a single circuit to the shed.
 
 