Electric box appears to be in wrong Place

Electric outlet rear is in shower framing. Seems wrong to me, but I know ZERO about this stuff. Builder says it is fine. Find it hard to believe you would have box under shower valve etc as shown. Appreciate your comments

Name:  a1.jpg
Views: 154
Size:  97.3 KB

Name:  a2.jpg
Views: 191
Size:  54.1 KB
 

Last edited by PJmax; 06-02-18 at 06:05 PM. Reason: reoriented pics
  #2  
Old 06-02-18, 04:57 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
There is no code issue. Pipes are run near wires and boxes all the time without issues.
 
  #3  
Old 06-02-18, 06:08 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,939
Received 3,952 Upvotes on 3,545 Posts
The box location is well within code. The only problem I can see there is the horizontal run of NM-b cable should have been centered in the stud.
 
 