mixed 12 and 14 gauge wire on 20 amp breaker

I am installing a new door where none existed and have to reroute a wire around the door. I noticed it was 14/2 and when I checked the circuit it was on there is a 20 amp breaker. I began to check to see what else was on that circuit and I came across a GFI in a bathroom that I am fairly certain is a 20 amp outlet and has 12 gauge wiring. Will changing to a 15 amp breaker be ok as far as safety is concerned?
 
Sponsored Links
  #2  
Old 06-11-18, 04:00 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,123
Received 71 Votes on 61 Posts
The breaker needs to be changed to protect the smallest conductors in the circuit. Change to a 15 amp breaker.
 
  #3  
Old 06-11-18, 07:53 PM
M
Member
Thread Starter
Join Date: May 2015
Location: u.s.
Posts: 85
Received 0 Votes on 0 Posts
Thanks for confirming that.
 
  #4  
Old 06-13-18, 09:45 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,173
Received 89 Votes on 84 Posts
PCBoss is correct, but by dropping the breaker to 15A you're creating a different code issue.

Bathrooms are supposed to be served by a 20A breaker.

Downsizing the breaker is most important to protect the wiring, but I would consider if there is any way to replace that length of incorrectly installed 14ga wire.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: