Tester says ground and hot are reversed -- doesn't look it

My electric socket tester shows that the hot and ground are reversed in a bedroom outlet. However, when I pulled the outlet from the wall, the hot wire was where it should be and the ground to the green screw. Any ideas what's wrong? Should I try installing a new outlet?
 
  #2  
Old 06-26-18, 12:59 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,495
Received 91 Upvotes on 83 Posts
That happens when the wires get crossed at an upstream outlet. It can take some time poking around to find where they goofed up.
 
  #3  
Old 06-26-18, 01:01 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,618
Received 74 Upvotes on 65 Posts
Do you have a multimeter? If so, I would suggest that you measure the outlet voltage using your multimeter. Set it to AC Volts, and a scale that is higher than 120V. Here's what you should expect to measure if the outlet is wired correctly:

Hot to Neutral: 120VAC
Hot to Ground: 120VAC
Ground to Neutral: 0VAC
 
  #4  
Old 06-26-18, 01:07 PM
J
Member
Thread Starter
Join Date: Jun 2018
Location: usa
Posts: 3
Upvotes: 0
Received 0 Upvotes on 0 Posts
Originally Posted by Astuff View Post
That happens when the wires get crossed at an upstream outlet. It can take some time poking around to find where they goofed up.
If the wires were crossed at an upstream outlet, wouldn't one of the other outlets show a fault also? None of the others in the house seemed to be wired incorrectly. Just trying to find a way to figure this out.
 
  #5  
Old 06-26-18, 01:18 PM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 27,089
Received 2,009 Upvotes on 1,801 Posts
It could happen if the wires are hooked up incorrectly from the upstream outlet in the circuit. If you plug the tester into the preceding outlet it could show correct because the incorrect wires are not providing power to that outlet.
 
  #6  
Old 06-26-18, 01:49 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Those testers are nice toys but can easily give incorrect readings. You need an analog (not digital) multimeter to get a true reading. Follow Bob's guide to expected readings in post #3.
 
  #7  
Old 06-26-18, 09:52 PM
R
Member
Join Date: Jun 2018
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Has anyone heard of a switch reversing polarity of outlet up the line. box has hot in hot out and switch leg. Out has correct polarity with switch off turn it on polarity swaps and burn up router. If i unhook switch leg at the light i have correct polarity. No junctions between switch and light. Is this an inadicate ground in the temp service
 
  #8  
Old 06-27-18, 08:33 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,495
Received 91 Upvotes on 83 Posts
R- Could be a MWBC with floating neutral.
 
  #9  
Old 06-27-18, 10:44 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,841
Received 178 Upvotes on 161 Posts
My electric socket tester shows that the hot and ground are reversed in a bedroom outlet. However, when I pulled the outlet from the wall, the hot wire was where it should be and the ground to the green screw. Any ideas what's wrong?

I think when you get a multimeter and test all wires you'll find you have an open neutral. Those plug-in testers leave a lot to be desired as far as accuracy, but are quick and easy. That's why building inspectors rely on them.
 
  #10  
Old 06-27-18, 11:13 AM
D
Member
Join Date: Apr 2014
Location: us
Posts: 1,323
Received 103 Upvotes on 97 Posts
I am from the old school. Connect a 120 volt bulb between a radiator in the room and first one wire then the other. The wire bulb lights on is 120 volt hot.
 
  #11  
Old 06-28-18, 07:31 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 9,785
Upvotes: 0
Received 45 Upvotes on 43 Posts
Hot/Ground reverse signal on a bug style tester is almost always actually an open/broken neutral. The plug in tester can't tell the difference.

Hot/ground reverse can't happen without some seriously screwed up dangerous wiring. Open neutral happens all the time from normal wear and tear of electrical devices. Much more likely outcome.
 
Gen voted this post useful.
  #12  
Old 07-02-18, 09:17 PM
R
Member
Join Date: Jun 2018
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Brand new wire no junction this is a home run box. I have an old panel feeding new panel temporary with 8-3 under a 40a breaker. New panel runs whole house except 220s. Original ground is #10 200a feeders
 
  #13  
Old 07-03-18, 12:21 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 9,841
Received 178 Upvotes on 161 Posts
Brand new wire no junction this is a home run box. I have an old panel feeding new panel temporary with 8-3 under a 40a breaker. New panel runs whole house except 220s. Original ground is #10 200a feeders
How is this related to this thread and the original poster? Did you have a question?
 
 