Tester says ground and hot are reversed -- doesn't look it

Tester says ground and hot are reversed -- doesn't look it

Reply

  #1  
Old 06-26-18, 11:56 AM
Member
Thread Starter
Join Date: Jun 2018
Location: usa
Posts: 3
Received 0 Votes on 0 Posts
Tester says ground and hot are reversed -- doesn't look it

My electric socket tester shows that the hot and ground are reversed in a bedroom outlet. However, when I pulled the outlet from the wall, the hot wire was where it should be and the ground to the green screw. Any ideas what's wrong? Should I try installing a new outlet?
 
Sponsored Links
  #2  
Old 06-26-18, 11:59 AM
Member
Join Date: Jun 2012
Location: USA
Posts: 1,412
Received 12 Votes on 11 Posts
That happens when the wires get crossed at an upstream outlet. It can take some time poking around to find where they goofed up.
 
  #3  
Old 06-26-18, 12:01 PM
Bob14525's Avatar
Member
Join Date: Jun 2013
Location: USA
Posts: 1,470
Received 11 Votes on 8 Posts
Do you have a multimeter? If so, I would suggest that you measure the outlet voltage using your multimeter. Set it to AC Volts, and a scale that is higher than 120V. Here's what you should expect to measure if the outlet is wired correctly:

Hot to Neutral: 120VAC
Hot to Ground: 120VAC
Ground to Neutral: 0VAC
 
  #4  
Old 06-26-18, 12:07 PM
Member
Thread Starter
Join Date: Jun 2018
Location: usa
Posts: 3
Received 0 Votes on 0 Posts
Originally Posted by Astuff View Post
That happens when the wires get crossed at an upstream outlet. It can take some time poking around to find where they goofed up.
If the wires were crossed at an upstream outlet, wouldn't one of the other outlets show a fault also? None of the others in the house seemed to be wired incorrectly. Just trying to find a way to figure this out.
 
  #5  
Old 06-26-18, 12:18 PM
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 20,796
Received 188 Votes on 175 Posts
It could happen if the wires are hooked up incorrectly from the upstream outlet in the circuit. If you plug the tester into the preceding outlet it could show correct because the incorrect wires are not providing power to that outlet.
 
  #6  
Old 06-26-18, 12:49 PM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Those testers are nice toys but can easily give incorrect readings. You need an analog (not digital) multimeter to get a true reading. Follow Bob's guide to expected readings in post #3.
 
  #7  
Old 06-26-18, 08:52 PM
Member
Join Date: Jun 2018
Posts: 2
Received 0 Votes on 0 Posts
Has anyone heard of a switch reversing polarity of outlet up the line. box has hot in hot out and switch leg. Out has correct polarity with switch off turn it on polarity swaps and burn up router. If i unhook switch leg at the light i have correct polarity. No junctions between switch and light. Is this an inadicate ground in the temp service
 
  #8  
Old 06-27-18, 07:33 AM
Member
Join Date: Jun 2012
Location: USA
Posts: 1,412
Received 12 Votes on 11 Posts
R- Could be a MWBC with floating neutral.
 
  #9  
Old 06-27-18, 09:44 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,978
Received 22 Votes on 17 Posts
My electric socket tester shows that the hot and ground are reversed in a bedroom outlet. However, when I pulled the outlet from the wall, the hot wire was where it should be and the ground to the green screw. Any ideas what's wrong?

I think when you get a multimeter and test all wires you'll find you have an open neutral. Those plug-in testers leave a lot to be desired as far as accuracy, but are quick and easy. That's why building inspectors rely on them.
 
  #10  
Old 06-27-18, 10:13 AM
Member
Join Date: Apr 2014
Location: us
Posts: 608
Received 4 Votes on 4 Posts
I am from the old school. Connect a 120 volt bulb between a radiator in the room and first one wire then the other. The wire bulb lights on is 120 volt hot.
 
  #11  
Old 06-28-18, 06:31 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Hot/Ground reverse signal on a bug style tester is almost always actually an open/broken neutral. The plug in tester can't tell the difference.

Hot/ground reverse can't happen without some seriously screwed up dangerous wiring. Open neutral happens all the time from normal wear and tear of electrical devices. Much more likely outcome.
 
  #12  
Old 07-02-18, 08:17 PM
Member
Join Date: Jun 2018
Posts: 2
Received 0 Votes on 0 Posts
Brand new wire no junction this is a home run box. I have an old panel feeding new panel temporary with 8-3 under a 40a breaker. New panel runs whole house except 220s. Original ground is #10 200a feeders
 
  #13  
Old 07-03-18, 11:21 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 9,978
Received 22 Votes on 17 Posts
Brand new wire no junction this is a home run box. I have an old panel feeding new panel temporary with 8-3 under a 40a breaker. New panel runs whole house except 220s. Original ground is #10 200a feeders
How is this related to this thread and the original poster? Did you have a question?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: