AC Problem

Need help figuring out problem. Main feed on sub panel has low voltage on 45volts on one leg coming in. Went to main panel and the feed breaker shows 120v on both outputs of the breaker. I measured neutral to main feed to output of the 200 amp breaker. I removed the low voltage feed wire at the sub panel and still read the low voltage. Could the Main 200 amp breaker be defective. I tried measuring a voltage drop across the the Main breaker and it read 0.0 Volts.
 
Sponsored Links
  #2  
Old 07-05-18, 02:14 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 55,253
Received 601 Votes on 566 Posts
Welcome to the forums.

Be very careful using your meter in the ohms setting when something is powered.
You should be measuring 240vac across the main breaker.
 
  #3  
Old 07-05-18, 03:20 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 3,819
Received 44 Votes on 42 Posts
When hot to neutral on one leg was 45 volts, what was hot to neutral voltage on the other leg at the same time?

You could have a bad neutral to that subpanel.

Do not touch meter leads to powered circuits when testing ohms or resistance or continuity.
 
  #4  
Old 07-05-18, 06:11 PM
C
Member
Thread Starter
Join Date: Jul 2018
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Yes one leg hot to neutral was 45 volts the other was 120 volts.
 
  #5  
Old 07-06-18, 08:28 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
This is probably a bad feeder breaker or cable. Were the measurements taken with electrical load on the service? I'm also not clear on exactly what is the main and sub on your descriptions.

Generally you would have a feeder from the power company, through the meter, then into a main breaker in the main panel. A feeder breaker in the main panel would energize a feeder cable to a subpanel which may or may not have a main breaker in it. Does the subpanel feeder cable run underground?

Exactly where are the measurements taken and which devices are/are not working?
 
  #6  
Old 07-07-18, 07:49 AM
C
Member
Thread Starter
Join Date: Jul 2018
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
The wiring is exactly as you've described. The meter readings were taken at the sub panel. The sub panel does have a main breaker So I took off the wires at the main breaker in the sub panel off and was reading 120v on one leg and 45v on the other. I went back to the main panel and read the power at the main breaker that feeds the sup panel and both legs read 120v under no load. The wire is 4 strands of 2AWG running underground that was just installed two months ago with no connections in between the main breaker and the sub panel main breaker. This has been working fine for the past two months. I went ahead and replaced the Feeder breaker in the main panel and the problem has gotten worse. Now Im reading at the sub panel 120v on one leg and 7v on the one that was reading 45v before. This is really baffling could it be a defective meter on the power pole?
 
  #7  
Old 07-07-18, 01:18 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,367
Received 48 Votes on 39 Posts
In your main panel, check voltage across the incoming feeders from the meter. Check ahead of the first main breaker. Check hot leg to hot leg, should read around 240 volts. Now, check each hot leg to neutral, each should read around 120 volts.

You asked:


This is really baffling could it be a defective meter on the power pole?

Is there a disconnect at the meter on the power pole? If so, check voltages at that breaker disconnect too, both before and after this disconnect breaker.
 
  #8  
Old 07-07-18, 01:47 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,028
Received 46 Votes on 41 Posts
It sounds awfully quick, but it sounds like one leg has gone bad underground .
 
  #9  
Old 07-07-18, 01:58 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,367
Received 48 Votes on 39 Posts
It sounds awfully quick, but it sounds like one leg has gone bad underground .

My first thought as well, but we know nothing about the type of wire or installation method that was used. I have even seen direct buried NM cable last 5 or 6 years without going bad. The same with NM cable strung through the trees, I was amazed. My father-in-law was unbelievably cheap.
 
  #10  
Old 07-07-18, 05:00 PM
C
Member
Thread Starter
Join Date: Jul 2018
Location: USA
Posts: 4
Received 0 Votes on 0 Posts
Ok read 240V across the two hot legs coming from the meter to the Main breaker, measured 120V on each leg to neutral on the breaker. the really weird thing is that I read 7V this morning at the sub panels main breaker one leg and this evening it was reading 97v until I applied a load and the it went to 5V.

The wire is four strands of aluminim 2AWG 150ft from the main panel to the sub panel buried 3ft underground in sand.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: