[img]http://i66.************/2yx0uuh.jpghttp://i66.************/2yx0uuh.jpg][img][IMG]http://i66.************/2yx0uuh.jpgeeplacing an old socket from my parents older 1920’s house. I have not pulled out the socket yet as I want to be sure I can just swap this out with another socket. Will attempt to upload a pic of this socket. Old socket has 4 prongs and the face is round. 2 stand blades on left and right, and the 2 smaller blades, one on top and bottom. Rewriting this circuit is out of the question. So my question, is there possibly no common wire within this socket? It would appear there is simply a hot going in 1 side and another hot going out
 

Last edited by drmax; 07-07-18 at 07:23 AM.
  #2  
Old 07-07-18, 05:19 AM
B
Member
Join Date: Jul 2018
Location: Virginia, USA
Posts: 13
Received 0 Votes on 0 Posts
I think we need that picture.
 
  #3  
Old 07-07-18, 08:01 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,293
Received 109 Votes on 101 Posts
My guess for now:

You may replace it with a modern 2 prong 15 amp duplex receptacle unit or 2 prong 120 volt 15 amp round single receptacle somewhat resembling it.

It has standard hot and neutral terminals (possibly both terminals or both terminal pairs gold, unpolarized, and interchangeable) One terminal or terminal pair connects to the left and top holes and the other terminal or pair connects to the right and bottom holes.

Back in the 1920's they also had (120 volt) plugs that fit just the top and bottom holes.
 
  #4  
Old 07-07-18, 09:57 AM
D
Member
Thread Starter
Join Date: Dec 2006
Location: usa
Posts: 169
Received 0 Votes on 0 Posts
Went to tiny pics to upload image to here. Used the correct settings and don’t seems to be working. Nice
 

Last edited by drmax; 07-07-18 at 10:23 AM.
  #5  
Old 07-07-18, 10:25 AM
D
Member
Thread Starter
Join Date: Dec 2006
Location: usa
Posts: 169
Received 0 Votes on 0 Posts
Can upload photo. Last try

 
  #6  
Old 07-07-18, 10:27 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,650
Received 48 Votes on 43 Posts
doityourself.com doesn't seem to like tinypic. replace the **** with tinypic dot com in the URL
 
Attached Images  
  #7  
Old 07-07-18, 10:35 AM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,650
Received 48 Votes on 43 Posts
Box is probably not properly grounded so replacing with a two prong duplex receptacle would be the easiest.
https://www.homedepot.com/p/Leviton-...-00W/100356969
 
  #8  
Old 07-07-18, 02:20 PM
D
Member
Thread Starter
Join Date: Dec 2006
Location: usa
Posts: 169
Received 0 Votes on 0 Posts
Any problem with just using a 3 prong as I already have one. Just label it “not grounded”
Also, then do I just hook one hot wire on one gold and the 2nd hot wire on the other gold, correct? This would complete the circuit as I think this is the way the old one is. My concern is, (and I have yet to remove it) but is it possible there is no neutral wires?
 
  #9  
Old 07-07-18, 02:51 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,763
Received 97 Votes on 87 Posts
Any problem with just using a 3 prong as I already have one. Just label it “not grounded”
Also, then do I just hook one hot wire on one gold and the 2nd hot wire on the other gold, correct? This would complete the circuit as I think this is the way the old one is. My concern is, (and I have yet to remove it) but is it possible there is no neutral wires?

If you question whether there is a neutral conductor you better halt all plans and do some checking before doing anything. Yes, it is entirely possible there is no neutral so do not install a 3 prong 125 volt receptacle without knowing what you are dealing with. It's also likely there is no grounding conductor so using a 3 prong receptacle is out of the question unless it is GFCI protected.
 
  #10  
Old 07-08-18, 07:29 AM
D
Member
Thread Starter
Join Date: Dec 2006
Location: usa
Posts: 169
Received 0 Votes on 0 Posts
Last question I think. Someone posted a pic of a home depot 2 prong. “If” there is no neutral, can I just go with that 2 prong outlet? There are several outlets in this house that have been replace over the years and they have 3 prong. I’m guessing my dad just didn’t hook up a ground to them. I know I don’t expect you guys to tell me to install a 3 prong without a ground...but I’m thinking it’d work just fine. There’s nothing internally to the outlet that wouldn’t allow it to work. I didn’t want to drive an hour to buy a 2 prong outlet, when the 3 will work. (probably more dangerous leaving this faulty ancient 2 prong installed).
 
  #11  
Old 07-08-18, 07:34 AM
D
Member
Thread Starter
Join Date: Dec 2006
Location: usa
Posts: 169
Received 0 Votes on 0 Posts
Post #6 there is a link that works of my .jpg that will show the old outlet. Unsure if anyone viewed it to show this relic
 
  #12  
Old 07-08-18, 07:54 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,293
Received 109 Votes on 101 Posts
In the U.S. all 120 volt circuits have one hot and one neutral. If there are indeed two hots either they are from different branch circuits (okay in one junction box) or have 240 volts between them.. I am quite sure that for your existing receptacle the two wires connected to the receptacle are hot and neutral although you should measure for good measure to see 120 volts between them.

You will have to find out which one is the neutral before installing the new 2 prong receptacle unit; the neutral is connected to the "silver" screw. Usually the neutral wire is white and in modern wiring the neutral must be white.

The technical name for "the neutral" is "grounded conductor." The two wires bringing 120 volts to the outlet box would both be hot except by convention and by code one is tied (bonded) to ground the correct location for that bond is at the first whole house disconnect breaker or switch. Assuming that all the connections are solid, voltage measured between neutral and a grounded object is almost zero at all times. Note that in old systems considered "ungrounded" the outlet box itself is not expected to be grounded by virtue of being tied to ground via some combination of wires, metal conduit, and other daisy chained junction boxes.

Meanwhile a neutral wire is not supposed to be used as a ground wire. By properly grounded we mean a circuit or system with a complete separate path back to the main disconnect as the ground path (equipment grounding conductor).

Three prong receptacles connected to ungrounded circuits by mistake can be grounded using a separately run ground wire down to the panel where the breaker for that circuit is located.
 
  #13  
Old 07-08-18, 09:25 AM
D
Member
Thread Starter
Join Date: Dec 2006
Location: usa
Posts: 169
Received 0 Votes on 0 Posts
Thx Allan for your post. New most of what you said. Were u able to view the pic in post #6? There is 124 vac between the 2 wires. As I look (without removing socket) behind as much as I can see, there is the one wire coming into the receptical box attached to one screw, then another wire going out the other side of the recept. That is attached to the other side of socket. Will assume that is daisy chained to another outlet in house. Could be possible there is another set of wires behind the outlet that is feeding the neutral, if it even exists. I know it is not 220 as we’ve used this in the past to operate hedge clippers. (this old wiring is about as big around as a mans little finger)
 
  #14  
Old 07-08-18, 10:07 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
You can't get 124v without a neutral or incorrectly used ground. The 120 volts is derived from one leg of the 240v supplied to your house and neutral (aka grounded conductor from the center tap of the secondary of the service transformer).
 
  #15  
Old 07-08-18, 12:02 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,293
Received 109 Votes on 101 Posts
Next try this:
Measure voltage from one of the receptacle wires to the edge of the box. Then measure from the other receptacle wire to the edge of the box. If you get approximately 120 volts for one measurement and also get approximately zero volts for the other measurement then label the wire that gave you the near zero measurement as the neutral. Now you can install the new receptacle.

If either or both of the measurements are not as I described then more tests are needed before you install the new receptacle.
 
  #16  
Old 07-08-18, 02:02 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,763
Received 97 Votes on 87 Posts
Measure voltage from one of the receptacle wires to the edge of the box.
But that is assuming the box is grounded. When the old receptacles like the OP showed us was used grounding conductors weren't used. 2 wires of the same color in the box back then might be 110 volts or might be 220 volts. Today, 120 or 240 volts. Still see some of those old receptacles with the original old wiring in a lot of the old turn-of-the-century houses in the older parts of most big cities.
 
  #17  
Old 07-08-18, 04:02 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Instead use a 3-wire extension cord plugged into a correctly grounded receptacle as your reference point. To determine neutral measure wide slot to each wire. The Wire that shows ~120v is hot. Try narrow slot to metal box to see if it is grounded. ~120v indicates grounded. There are other ways but that should work.
 
  #18  
Old 07-11-18, 05:08 AM
D
Member
Thread Starter
Join Date: Dec 2006
Location: usa
Posts: 169
Received 0 Votes on 0 Posts
Voltage

measured voltage again. 116 vac between the 2 wires. As someone suggested to plug in a drop cord in socket, that won’t work because the outlet is faulty. Have a local guy near by that I will ask.
 
  #19  
Old 07-11-18, 06:15 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,293
Received 109 Votes on 101 Posts
Plug the drop cord in a different socket, er, receptacle, that is properly grounded.

To find the neutral, test using the wires attached or formerly attached to the old receptacle, not the holes in the receptacle. (You can test using the terminal screws of the old receptacle if the wires have not yet been unhooked.)

If the box was not grounded then you will not get about 120 volts from one old receptacle wire to the lip of the box and also about zero volts from the other old receptacle wire (the neutral) to the box as I had suggested earlier. Then you would need the drop cord.
 

Last edited by AllanJ; 07-11-18 at 06:30 AM.
 