Running a neutral line

I went to install a electronic timer switch, and discovered that there is no neutral line (white) to the existing switch.

I was going to run a neutral from a different outlet, but wanted to double check that it is ok, since the existing wires seem to come from a different direction.

I wanna run the neutral from this outlet since it's closer and access is easier.

Thanks!
 
  #2  
Old 07-15-18, 06:08 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,811
Received 3,922 Upvotes on 3,518 Posts
You cannot run just a neutral wire. The wiring must remain in one jacket.
Why not use a timer that doesn't require a neutral. Do you want a recommendation ?
 
  #3  
Old 07-15-18, 10:24 PM
G
Member
Thread Starter
Join Date: Apr 2010
Location: USA
Posts: 48
Upvotes: 0
Received 0 Upvotes on 0 Posts
It's a vacation property that we own. The switch is for a ice eaves wire, and I'd like to set it on a regular schedule, since we won't be in the house regularly.

There are two switches...for one of them, I think I can run a new romex, the second one may be a bit more challenging, so I'll have to investigate more.

The previous owner was an electrician, so there is a bunch of custom stuff that has me scratching my head
 
  #4  
Old 07-15-18, 10:32 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Are you saying there is a receptacle for the eve heaters? If so and power comes in there you need to replace the 2-conductor cable to the switch with a 3-conductor cable.
 
  #5  
Old 07-15-18, 11:02 PM
G
Member
Thread Starter
Join Date: Apr 2010
Location: USA
Posts: 48
Upvotes: 0
Received 0 Upvotes on 0 Posts
Correct, I'm replacing a existing switch (one of those that you turn a rotary dial to the desired time).

I'll see if I can fish a new wire to the existing switch.
 
  #6  
Old 07-16-18, 12:18 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
I'll see if I can fish a new wire to the existing switch.
You can't fish a wire. It must be a 3-conductor cable.
 
  #7  
Old 07-16-18, 05:06 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,073
Received 161 Upvotes on 147 Posts
Hi, it seems a bit odd to put gutter heat on a timer, how are you going tell when and if they need to be on?
Just curious.
Geo
 
  #8  
Old 07-16-18, 08:31 AM
G
Member
Thread Starter
Join Date: Apr 2010
Location: USA
Posts: 48
Upvotes: 0
Received 0 Upvotes on 0 Posts
Geo, you're right, it is a bit odd, but I won't be there to know if I need it, and I'd rather be safe than have the gutters all messed up, it'll be on during the cold months so, I'm not terribly worried.
 
  #9  
Old 07-16-18, 10:24 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 6,086
Received 419 Upvotes on 372 Posts
Have you considered an automatic water/temperature-sensing switch?

Like this:
https://www.amazon.com/Easy-Heat-RS-.../dp/B000BMABZG

(This one has a lot of poor reviews, but there are probably better ones out there)
 
  #10  
Old 07-18-18, 09:43 AM
G
Member
Thread Starter
Join Date: Apr 2010
Location: USA
Posts: 48
Upvotes: 0
Received 0 Upvotes on 0 Posts
I was able to get this to work for one switch.

For the other switch, it is controlling an outlet outside, and hence doesn't have a "load" wire, just a neutral and a hot, and the switches I bought need all three.

the challenge here is that the run to the outlet is long, and I'm not sure if i can access all of it. What happens if I run a new romex from a close by outlet, just for the neutral line (and cap off the rest). Does the neutral actually need to run to the outlet itself?
 
  #11  
Old 07-18-18, 12:27 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
What happens if I run a new romex from a close by outlet, just for the neutral line (and cap off the rest). Does the neutral actually need to run to the outlet itself?
All conductors must be in the same raceway or sheath. You need to abandon the 2-conductor cable and replace with a 3-conductor cable or use a device that does not use a neutral.
 
 