irrigation pump timer


  #1  
Old 07-20-18, 10:17 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
irrigation pump timer

Hello,

Looking for an irrigation pump timer, preferably digital.

Currently have 1.5 HP Goulds Irrigator. Wired 240v. Thinking of upgrading to GT 20 2HP, so the ability to also use on that potential pump would be good.

What I have found so far is the Intermatic EH40. However, this is only rated to 1.5HP so that would limit me going to the GT 20.

Thanks in advance.
 
  #2  
Old 07-21-18, 02:50 AM
pugsl's Avatar
Forum Topic Moderator
Join Date: Mar 2008
Location: United States
Posts: 8,161
Received 77 Upvotes on 70 Posts
Here is a whole page of timers to look at.
https://www.google.com/search?q=240+...hrome&ie=UTF-8
 
  #3  
Old 07-21-18, 03:48 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Hi, do you also control your zones from this timer?
Geo
 
  #4  
Old 07-21-18, 09:25 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
You won't find the heavier current capacity on the lower priced units. Personally I don't find that any of these timers hold up well switching heavy loads. I use basic timer modules to control a contactor. A little more work in setup as the system would need to be assembled but much longer lasting.

This is one of the higher current digital timers from Intermatic.
Intermatic-ET8215C-Electronic-Astronomic-Timeclock
 
  #5  
Old 07-21-18, 10:38 AM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Not sure why but I am unable to reply to individual posts.

Thanks pugsl. I saw all of these but was hoping to get some feedback on ones the professionals on this site may use.

Geochurchi, I only have (1) zone of 11 Rainbird rotors off a 2" PVC line that runs the back, side and front of my lot (on a corner). Flip a switch and they all turn on at once.

Pete, thanks for the link and information on the set-up you use.
 

Last edited by 7474; 07-21-18 at 11:54 AM.
  #6  
Old 07-21-18, 11:27 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
Like I mentioned..... I do not use any of those types of timers for heavy loads.
 
  #7  
Old 07-21-18, 11:55 AM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Pete, could you please assist me with the basic timer and contactor set-up that I could use? Thanks.
 
  #8  
Old 07-21-18, 03:02 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
There are many combinations available. I use a certain 12vdc timer module but that requires a power supply from 240vac to 12vdc. In your case it would be easier to use a self container 240v timer like in the following link.
ebay/LCD-Digital-Control-Power-Programmable-Timer-Weekly-16A-Time-Relay-Switch

As far as a contactor.... search for 2 pole 240v contactor 240vac coil.
Here's one from the depot that would be perfect. Get several. When one wears out... replace it.
Packard-208-240-Volt-Coil-Voltage-F-L-Amp-30-Pole-2-Res-40-Amp-Definite-Purpose-Contactor
 
  #9  
Old 07-21-18, 05:05 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
So you flip a switch and the zone comes on, does this switch also control the pump?
Geo
 
  #10  
Old 07-21-18, 08:06 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Geo...
I flip a switch in the garage, turns on the pump at the lake, supplies water to all 11 rotors at the same time. There is only 1 zone of 11 rotors.
 

Last edited by 7474; 07-21-18 at 08:23 PM.
  #11  
Old 07-21-18, 08:12 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you Pete. I appreciate the assistance.
 
  #12  
Old 07-22-18, 04:01 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
OK GOT IT! Here is another option with less parts, rated for 3HP.
https://images.homedepot-static.com/...389a7bf647.pdf
Just a thought.
Geo
 
  #13  
Old 07-22-18, 09:12 AM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Geo. I had seen those previously and was turned off by the price (~$200). Although, I looked again and found 2hp versions without rain sensor for $50 at HD. The one I had previously looked at was a 3hp with rain sensor.

The saving money side of me would like to go with Pete's version. However, I am a visual guy and haven't been able to find a wiring diagram for how I would set-up.

Thanks again for everyone's assistance.
 
  #14  
Old 07-24-18, 11:58 AM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Could either of these be used in conjunction with the contactor for creating a pump timer? Thanks.


https://yourhome.honeywell.com/en/pr...witch-rpls540a

https://customer.honeywell.com/en-US...uct.Rank&asc=1
 
  #15  
Old 07-24-18, 01:55 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Either could be used, as long as the coil voltage on the contactor is 120 volts, IMO a single irrigation timer would be a lot easier, unless you are planning to remote mount that switch.
Geo
 
  #16  
Old 07-24-18, 02:06 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the reply.

I’m starting to think also that the single switch would be easier, although pricier. Especially since I would like a digital timer.

Thanks again for everyone’s input/assistance.
 
  #17  
Old 07-24-18, 03:00 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Also, I have both of those switches and they are not currently being used. Again, appeals to my value side.
 
  #18  
Old 07-24-18, 04:08 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
Both of those timers you linked to require 120vac..... so make sure you have a 120v at your pump.
 
  #19  
Old 07-24-18, 04:27 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Pete.

The pump is 240, but there is 120 also available.

I assume the 240 line is one end of the contactor and the 240 load is the other end? Is the timer wired into the sides of the contactor?

Thanks for your continued help.
 
  #20  
Old 07-24-18, 05:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
240v line goes to the L1 and L2 connections. Pump/load connects to T1 and T2.
The timer will connect to the coil. Those connections are on the side.
Since you will be using a 120v timer..... you'll need a contactor with a 120vac coil.
 
  #21  
Old 07-24-18, 06:52 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks Pete.

Something like this.....

Packard Online Item Details

or this....

http://www.packardonline.com/Shop/Product/2508
 

Last edited by 7474; 07-24-18 at 07:29 PM.
  #22  
Old 07-24-18, 08:22 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
Yessir..... both would work fine.
 
  #23  
Old 07-24-18, 08:34 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Pete, thank you very much.

Hopefully, last question on this thread. Is this how the timer would be wired to the contactor (besides that it shows 3 phase)?

Name:  86B1B92B-1C71-412C-A0CF-42AECC06A2B5.jpg
Views: 316
Size:  20.7 KB
 
  #24  
Old 07-24-18, 08:51 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Yes, that is correct. ............
 
  #25  
Old 07-24-18, 09:07 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thank you very much, greatly appreciate all the assistance.
 
  #26  
Old 07-27-18, 05:27 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Where do the 240v grounds connect to the contactor?
 
  #27  
Old 07-27-18, 05:43 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Assuming you mounted the contactor in a metal enclosure you would attach the grounds to a lug installed in the box after scraping any paint off first.
Geo
 
  #28  
Old 07-27-18, 05:50 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
It is mounted in a Plastic junction box not a metal box.
 
  #29  
Old 07-27-18, 05:55 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Good move on the plastic, I would try to attach it to the base of the contractor, use a small lug.
Geo
 
  #30  
Old 07-27-18, 06:30 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Here was my solution????

Name:  D5EE190C-7B79-48F4-A95C-E4F6D8E71E13.jpg
Views: 180
Size:  12.9 KB
 
  #31  
Old 07-28-18, 04:07 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
I might have put a small nut and bolt and washer through one of the holes in the contactor base, theoretically a screw is only supposed used for one purpose.
Geo
 
  #32  
Old 07-28-18, 01:38 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the reply.

I will go back and change it out.

Does the 120 V connect to the contactor on opposite sides or the same side? I’ve seen it both ways, but more frequently opposite sides.
 
  #33  
Old 07-28-18, 02:33 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
One side should be the neutral and the other is the feed from the timer.
Geo
 
  #34  
Old 07-28-18, 03:10 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 64,928
Received 3,947 Upvotes on 3,540 Posts
Usually there is a double slide contact on both sides.
Some do connect to one side but will be labeled that way.
There is no polarity to the connections.
 
  #35  
Old 07-29-18, 07:52 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the continued assistance.

I believe the project is a success. The timer is operational.

Originally, the pump switch shared a 2 gang PVC box with a GFCI outlet. The box measured 4.5 x 4.5 x 2, not enough room for the contactor. So, I added a 6 x 6 x 4 junction box to the front of the original box. I cut out the back of the larger box and attached it to the original box. May not be the prettiest, but it sits on the side wall of the garage right by the radon pipe so it doesn’t stick out an unsightly amount.

I had to go with a different timer as the ones I had were no neutral and required a minimum amount of constant wattage to power them. This timer has a neutral and is powered off the load side of the GFCI so I also have that added protection.

I have attached a photo of my final product. As well, there’s a photo of my fixed grounding lug.

Again, thanks for all of the assistance.

Name:  20BC57A5-D33B-4A44-A86D-8FFE9DCCED21.jpg
Views: 135
Size:  8.6 KB

Name:  1AE027A6-774F-4B6A-B230-FD35EDA6E199.jpg
Views: 124
Size:  11.4 KB
 

Last edited by 7474; 07-29-18 at 08:10 PM.
  #36  
Old 07-30-18, 04:18 AM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
Thanks for the report.
Geo
 
  #37  
Old 07-30-18, 07:23 AM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
The GFCI was a 20amp breaker with 12ga wire. The timer is 15amp.

I have read that it is not permitted to have the 15amp timer on a 20amp breaker. However, I have also read that it is permissible if it is not the only thing on the circuit.

I changed the breaker to a 15amp to be safe until I found out more.

If the 15amp timer is permitted on the 20amp circuit, can I use 14ga wire to connect the timer to the GFCI receptacle and the contactor?

Thanks
 
  #38  
Old 07-31-18, 04:18 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Bump for any assistance w previous post. Thanks.
 
  #39  
Old 07-31-18, 05:36 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 5,074
Received 161 Upvotes on 147 Posts
15 Amp receptacle on a 20 Amp circuit is fine as far as I know,and the timer as well, you could leave the 15Amp breaker for the circuit, I would use #12 for the complete circuit.
Geo
 
  #40  
Old 07-31-18, 08:47 PM
7
Member
Thread Starter
Join Date: Feb 2007
Location: USA
Posts: 70
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the reply.

I would like like to change it back to the 20amp because the GFCI is used for powering various wood working power tools. However, need to continue to research the ability to use the 15a timer on the 20a circuit.

Also, would like to keep the 14g as that is the only stranded wire I have. I believe u can only use stranded wire with the quick disconnects that the contactor requires for the coil. I will have to continue to research the use of solid vs stranded with the quick disconnects.

 
 