Looking for info on putting power to a shed.

I need to run electrical to my shed. Rather than running individual wiring for each thing, I wondered if itís possible to run a separate small breaker box in the shed. Our cottage has a main breaker panel of 100 amp. In the shed I will have a refrigerator, lights, some outlets, and an electric dryer. Can someone give me info on what size breaker I would need in the panel and what size wiring to run to the shed to supply a small breaker box?
 
Sponsored Links
  #2  
Old 07-25-18, 07:37 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,943
Received 43 Votes on 41 Posts
If you plan to have an electric dryer I recommend at least a 60A breaker panel for the shed. That would require wiring of #6 copper or #4 aluminum, but larger might be required if the distance is more than about 100 feet. The shed subpanel needs a four wire feeder, separate ground and neutral bus bars and a ground rod bonded to the ground bus with #6 copper.
 
  #3  
Old 07-25-18, 07:51 AM
JulietCapulet's Avatar
Member
Thread Starter
Join Date: Nov 2007
Location: USA
Posts: 57
Received 0 Votes on 0 Posts
Thank you for that info. So if I understand correctly I am running 6/3 wire with ground from the main panel to the shed, which is less than 100 feet away, and connecting it to a 60 amp box. The circuit breaker in the main panel would be a double pole 60 amp? I also did not realize I would need to put in a separate grounding rod.
 
  #4  
Old 07-25-18, 08:16 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,943
Received 43 Votes on 41 Posts
Yes 6/3g UF-B can be direct buried (not regular romex NM-B!) at 24" deep to the shed. Use a conduit sleeve for protection of the cable from the building down to the bottom of the trench. In the shed you need a box that is at least 60A but can be bigger. You don't need a main breaker in the shed if there are 6 or fewer circuits. A single circuit to an outbuilding would not require a ground rod, but a panel does.
 
  #5  
Old 07-25-18, 10:39 AM
JulietCapulet's Avatar
Member
Thread Starter
Join Date: Nov 2007
Location: USA
Posts: 57
Received 0 Votes on 0 Posts
Thank you so much!!! I know you said 60 amp minimum or larger in the shed. I assume that whatever amp box I get must be the size of the breaker that I put in the main panel to run the power out there. Is that correct?
 
  #6  
Old 07-25-18, 11:31 AM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,479
Received 111 Votes on 87 Posts
You can use a 100A main breaker panel in the shed if you like even though it's fed by a 60A breaker at the house. Those are more common and sometimes the cheapest way to go.
 
  #7  
Old 07-25-18, 01:57 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
And a main breaker panel kit comes with an assortment of branch circuit breakers making it a good bargain. The main breaker in the subpanel is used only as a disconnect so using a 100a panel is no problem.
 
  #8  
Old 07-25-18, 06:35 PM
JulietCapulet's Avatar
Member
Thread Starter
Join Date: Nov 2007
Location: USA
Posts: 57
Received 0 Votes on 0 Posts
As always, you guys are amazing! I find so much advice on this site and I truly truly appreciate it. Thank you all for everything you do!
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: