Replacing switch with timer issue.

Reply

  #1  
Old 07-25-18, 04:34 PM
S
Member
Thread Starter
Join Date: Jan 2012
Location: Canada
Posts: 9
Received 0 Votes on 0 Posts
Replacing switch with timer issue.

We have a switch operating an exterior light with power being carried on via the 3 wire from switch to 3 separate plugs on deck. All operates fine until I replace switch with Leviton timer. Tester shows "open neutral" but does NOT show that if simple paddle switch is left in.
 
  #2  
Old 07-25-18, 04:40 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,786
Received 1,324 Votes on 1,224 Posts
We'd need to know what you have for wiring at the switch.
Is it JUST a single three wire cable ?
If yes.... one wire will be hot, white will be neutral and the third wire is switched.
 
  #3  
Old 07-25-18, 05:33 PM
S
Member
Thread Starter
Join Date: Jan 2012
Location: Canada
Posts: 9
Received 0 Votes on 0 Posts
14/2 coming in direct from pony panel in garage...14/3 going to light fixture...14/2 from light fixture to remaining plugs.
When I had simple switch wired up...whites married off together, black in and black out to one terminal on switch and red to the other terminal...everything works fine.

when I replace with a timer trouble arises.
 
  #4  
Old 07-25-18, 06:14 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
If I'm following you and light is before the receptacles.

Power im black pigtailed to timer line in and black of 3-conductor cable.
Red of 3-conductor cable to timer load out.
All whites together.
Red and white to lights.
Black and whites out to first receptacle.

If your switch was intended for either a single switch situation or a 3-way switch you may have a wire left over unused.
 

Last edited by ray2047; 07-25-18 at 07:04 PM.
  #5  
Old 07-26-18, 04:58 AM
S
Member
Thread Starter
Join Date: Jan 2012
Location: Canada
Posts: 9
Received 0 Votes on 0 Posts
You are correct regarding sequence of fixtures and that is switch - light - receptacle.

Would I treat this is a 3-way situation? I have followed the Leviton instructions as if it's a 3way so perhaps that's my issue...there is NOT a second switch beyond the light.

I will try your suggestion today...thx for your attention.
 
  #6  
Old 07-26-18, 05:03 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
If there is only one switch it is not a 3-way. If you tell me the colors on the timer and their function I can give you a diagram if needed.
 
  #7  
Old 07-26-18, 05:07 AM
S
Member
Thread Starter
Join Date: Jan 2012
Location: Canada
Posts: 9
Received 0 Votes on 0 Posts
Timer has black, white, red, yellow (apparently for 3way use) and green(ground).

I have black and white into switch box and black, red and white going out to light.
 
  #8  
Old 07-26-18, 06:34 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Here is a diagram to try:
 
Attached Images  
  #9  
Old 07-26-18, 10:26 AM
S
Member
Thread Starter
Join Date: Jan 2012
Location: Canada
Posts: 9
Received 0 Votes on 0 Posts
BINGO!!! Thanks very much for your help...much appreciated!!!
 
  #10  
Old 07-26-18, 10:45 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Glad you got it. Thanks for letting us know.
 
 