Wall Oven Question


  #1  
Old 08-18-18, 06:45 PM
E
Member
Thread Starter
Join Date: Aug 2018
Posts: 1
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wall Oven Question

I’m a little confused...

i did the rough in electrical work for work for my new house prior to picking out any appliances. We planned on doing a wall oven so researched and it seemed like they were either 30 amp or 40 amp (depending on single or double) so I went ahead and ran an 8/3.

Received the wall oven this weekend and on the serial plate says 3.7kw @ 240. Manual that came with wall oven said look at serial plate and gave a table....table recommended 20 amp circuit for anything less than 4800.

Does this seem right? I know the wattage matches up but was fully expecting to put in a 30 amp two pole. Just wanted to make sure before I head to Menards to swap my 2 pole 30 for a 2 pole 20.

Any issues with throwing a 20 amp breaker on the 8/3 line?
 
  #2  
Old 08-19-18, 04:41 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,093
Received 786 Upvotes on 666 Posts
If it is only a recommendation of the circuit size in the manual then I would just use the 30 amp breaker. You are protecting the wire, not the oven.

If the manual said you must use a 20 amp breaker, then you would have to follow their requirement.
 
  #3  
Old 08-19-18, 01:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,142
Received 3,619 Upvotes on 3,245 Posts
I'd recommend using a 2P20A breaker for that oven. A 20A breaker on 30A wire is ok.
 
 