Wall Oven Question
#1
Member
Thread Starter
Join Date: Aug 2018
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Wall Oven Question
I’m a little confused...
i did the rough in electrical work for work for my new house prior to picking out any appliances. We planned on doing a wall oven so researched and it seemed like they were either 30 amp or 40 amp (depending on single or double) so I went ahead and ran an 8/3.
Received the wall oven this weekend and on the serial plate says 3.7kw @ 240. Manual that came with wall oven said look at serial plate and gave a table....table recommended 20 amp circuit for anything less than 4800.
Does this seem right? I know the wattage matches up but was fully expecting to put in a 30 amp two pole. Just wanted to make sure before I head to Menards to swap my 2 pole 30 for a 2 pole 20.
Any issues with throwing a 20 amp breaker on the 8/3 line?
i did the rough in electrical work for work for my new house prior to picking out any appliances. We planned on doing a wall oven so researched and it seemed like they were either 30 amp or 40 amp (depending on single or double) so I went ahead and ran an 8/3.
Received the wall oven this weekend and on the serial plate says 3.7kw @ 240. Manual that came with wall oven said look at serial plate and gave a table....table recommended 20 amp circuit for anything less than 4800.
Does this seem right? I know the wattage matches up but was fully expecting to put in a 30 amp two pole. Just wanted to make sure before I head to Menards to swap my 2 pole 30 for a 2 pole 20.
Any issues with throwing a 20 amp breaker on the 8/3 line?
#2
If it is only a recommendation of the circuit size in the manual then I would just use the 30 amp breaker. You are protecting the wire, not the oven.
If the manual said you must use a 20 amp breaker, then you would have to follow their requirement.
If the manual said you must use a 20 amp breaker, then you would have to follow their requirement.