230v Special Electrical Outlet?
#1
Member
Thread Starter
Join Date: Sep 2018
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
230v Special Electrical Outlet?
So I ordered a window AC unit from Amazon, refurbished, super good price, it said it needed a special 20amp electrical outlet. I'm figuring it's the normal 20amp outlet where the left prong is horizontal. Turns out, the plug looks exactly like that, but it's the right side that's horizontal, not the left side. I cannot find this outlet ANYWHERE. Checked Lowes, Home Depot, online, I just have no idea where to find it. I've looked up 20amp, 230v, AC outlet, etc, can't find anything.
Can somebody please help me find this. The breaker box it's getting hooked up to is in my garage, all 20/30 amp breakers so I'm sure it can handle it. I just can't find the outlet to wire the damn thing up.
Can somebody please help me find this. The breaker box it's getting hooked up to is in my garage, all 20/30 amp breakers so I'm sure it can handle it. I just can't find the outlet to wire the damn thing up.
#2
Member
What you need is NEMA 6-20R and that outlet is readily available at any hardware stores. You are probably confused because those outlets are made to accept both 15A and 20A plugs.
It accepts plugs with both prongs horizontal (240V 15A) and plugs with only right side horizontal (240V 20A).
https://www.homedepot.com/p/Leviton-...-0WS/100356999
You will have to run a dedicated 12-2 cable from the breaker panel and feed it with 2 pole 20A breaker. Most likely you will need to add a breaker.
You can wire both white and black wires to each pole of 2 pole breakers. You also need to mark white wire with electric tape or some other means to mark it as hot (although most people never do).
It accepts plugs with both prongs horizontal (240V 15A) and plugs with only right side horizontal (240V 20A).
https://www.homedepot.com/p/Leviton-...-0WS/100356999
You will have to run a dedicated 12-2 cable from the breaker panel and feed it with 2 pole 20A breaker. Most likely you will need to add a breaker.
You can wire both white and black wires to each pole of 2 pole breakers. You also need to mark white wire with electric tape or some other means to mark it as hot (although most people never do).
#3
Member
Thread Starter
Join Date: Sep 2018
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Nope, that's the one I just bought and have to go return... I need that outlet but flip flopped horizontally. The Right side of the outlet needs to be horizontal, not left side.
#4
It looks like an Amana PTAC uses that configuration.
Amana Air Conditioners - Heat-Pump, Electric Heat, PTAC, 26" AC, RAC
Amana Air Conditioners - Heat-Pump, Electric Heat, PTAC, 26" AC, RAC
Last edited by PJmax; 09-01-18 at 05:09 PM.
#6
Member
Thread Starter
Join Date: Sep 2018
Location: USA
Posts: 3
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I am such an idiot. I looked at that link like 5 times and just now noticed it's what I needed. Too much work and not enough sleep... Thank you guys very much. I wish there was an extension cord like that 6-20R but I suppose running another outlet isn't that big of a deal!
#8
Member
I wish there was an extension cord like that 6-20R but I suppose running another outlet isn't that big of a deal!
Do you already have a 240V outlet nearby?
#9
Member
Join Date: Sep 2015
Location: United States
Posts: 1
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Definitely get the 6-20R if its a 240V circuit/appliance. My son recently smoked his x box while staying at my grandmothers after she died. My deceased grandfather knew just enough electric work to be dangerous (we called him Rube Goldberg) Lol! They had a long gone 240V window unit but the receptacle remained which was a 20A 120V, Im guessing he changed the cord plug just to get it working quickly without hunting down parts. While hospice was at their house the 120V oxygen concentrators kept blowing while plugged into that same outlet, Im surprised they worked that long. Some switch mode power supplies are 120V 220V rated but some arent. Suprised my grandmother never plugged her old Electrolux canister vac into that circuit. Would have sucked real good for a few seconds followed by burning magnet wire or disintegrated rotor/fan impeller!