Extending Ungrounded Cable

Seperated from: https://www.doityourself.com/forum/e...conductor.html

I have a 1960's era room which was added on to a 1950's era house. Inside there is a 1 gang metal receptacle which is powered via a 12/3 Romex which has a white, black, and red wire. There is no ground wire but the red is attached to the ground screw. They used to sell 3 wire Romex without a dedicated grounding wire and it appears that they might have simply used the red wire as a ground. I want to connect to this a GFCI receptical on the exterior side of the wall. Please advise.
 

Last edited by ray2047; 09-09-18 at 04:15 PM.
  #2  
Old 09-09-18, 04:20 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
Ungrounded cables can not be extended. Grounds #6 and smaller must be factory green. Other colors can't be used.
 
  #3  
Old 09-09-18, 04:28 PM
P
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Electricity doesn't know the color so let's pretend that it's green. . How can I test if the red wire is performing the grounding function?
 
  #4  
Old 09-09-18, 04:35 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 60,854
Received 1,336 Votes on 1,234 Posts
To answer your question directly.....you can measure from black to red and you should measure 120vAC.
 
  #5  
Old 09-09-18, 05:16 PM
P
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
Measuring across black to red lit up the 110v light on my probe so I can assume it's grounded and it would support running an additional exterior GFCI receptacle?
 
  #6  
Old 09-09-18, 06:52 PM
J
Member
Join Date: Jan 2011
Location: USA
Posts: 4,857
Received 83 Votes on 78 Posts
#1, Use a real volt/OHM meter not a trouble light!
 
  #7  
Old 09-09-18, 07:04 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,803
Received 252 Votes on 220 Posts
A GFCI does not need a ground in order to function.
 
  #8  
Old 09-09-18, 07:05 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,583
Received 13 Votes on 11 Posts
You don't need a ground for a GFCI to work but using the red is a code violation. 110v is low but acceptable. Usually it should be close to 120v.
 
  #9  
Old 09-09-18, 07:07 PM
P
Member
Thread Starter
Join Date: Jan 2015
Location: USA
Posts: 5
Received 0 Votes on 0 Posts
OK, my meter measures 121.9
 
 