When framing around the electrical and I would like the box to be flush with the finished wall. However, this means the wiring coming into the cabinet (especially the main feed) will be right behind the finished wall. I know code states that a nail plate has to be used when the wiring is < 1 1/4" from the finished wall when going through a stud, so is there the same type of restriction for this?
 
Attached Images  
  #2  
Old 09-14-18, 02:32 PM
L
Member
Join Date: Nov 2015
Posts: 1,550
Received 92 Votes on 80 Posts
Nail plates are required only on the stud to protect wires from screws or nails driven on to the stud.

The panel can sit a little deeper than drywall (most panels covers can handle 1/4" or some even up to 1/2").

If you have a cable or phone lines spliced near the panel, it is better to build a electrical cabinet instead of covering all up.

Don't forget to put fire stop on top of the studs.
http://www.ifinishedmybasement.com/f...nt/fire-block/
 
  #3  
Old 09-14-18, 02:59 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,794
Received 252 Votes on 220 Posts
(most panels covers can handle 1/4" or some even up to 1/2").
Panels should be flush or 1/8" set back from the face of the drywall.
 
 