I had power dropped on my property and it is 350' to our build site. I want 200amp service at the house. what is my voltage drop going to be for the long run to the house, and what are the potential hazards for such drop? I had planned on running aluminum 4/0 4/0 2/0. I found an online calculator that indicated my voltage drop would be 2.86% based on 240v, AC single phase, single set of conductors at a load current of 200 amps. Do I need to worry about this? Should I have the power company move my meter base next to the house?
 
Sponsored Links
  #2  
Old 09-26-18, 05:31 PM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,505
Received 17 Votes on 17 Posts
The 2.86% voltage drop at 200 amps is not a problem.

Your choice, probably depending on cost. You would have to pay for the line from the present proposed meter location over to the new meter base at your house plus a separate pole transformer nearby. This line would be a medium tension (primary) line to eliminate the voltage drop problem.

Otherwise the long fat 120/240 volt line you first suggested has no greater hazard compared with a shorter skinnier line carrying the same voltage in the same manner (underground; overhead). If there is a whole house disconnect switch or breaker out at the meter base then you need a fourth conductor for ground running to the house panel regardless of distance.
 
  #3  
Old 09-26-18, 05:46 PM
Member
Thread Starter
Join Date: Sep 2018
Location: usa
Posts: 3
Received 0 Votes on 0 Posts
Thanks. I am assuming I had all my factors correct that I plugged into the online calculator, and if so i take it the 6.86v drop is nothing to worry about. I forgot to mention I would pull a ground wire as well.
 
  #4  
Old 09-26-18, 06:33 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,933
Received 55 Votes on 48 Posts
Your load will not be 200 amps, that is the max rating of the breaker. You need to do a load calculation to determine the load that will be on the feeder. Voltage drop is calculated by voltage, current, distance, and wire material.
 
  #5  
Old 09-26-18, 10:20 PM
Member
Thread Starter
Join Date: Sep 2018
Location: usa
Posts: 3
Received 0 Votes on 0 Posts
Thank you, based on a formula I found online my load current came out to about 120 amps. that puts my voltage drop at 2.7%. We have no furnace, use wood heat, and my water pump runs off solar power. Oven / stove are gas, biggest appliance is water heater and dryer.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: