how many cables per 3/4 drilled holes in joists?

Can I put 3 14/2 or 3 12/2 cables in a 3/4 bored hole without having to derate?
They will run more than 24", probably throughout the length of the floor of apartment before splitting off to the relevant rooms.
 
Sponsored Links
  #2  
Old 09-27-18, 04:54 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,661
Received 220 Votes on 194 Posts
The code says you have to start derating when the current carrying conductors is more then 3 in a group. This includes cables. However, derating doesn't really effect anything untill you get to more then 9 current carrying conductors when using wire and cables with a 90 degree insulating rating.

To answer your question directly: Yes, 3 cables is fine. Of course my info is based on the NEC.
 