Breaker panel.
My 1/3 hp septic tank effluent pump blew and I replaced it with a 1/2 hp model and replaced the float switch at the same time. For some unknown reason it was/is powered by a 15 amp dipole breaker along with several receptacles, light fixtures and outlets. Doesn't sound like 'code of the west' to me. Anyway the new 1/2 hp doesn't care for this breaker and tends to pop if regularly. I need a breaker with more amps but the box has no empty slots. Is it worthwhile to replace the 15 amp dipole, leaving the circuits in place, with something stouter and, if so, how stout? I have a couple of 30 amp breakers in my shop but the distance is about 150 ft - too far?
#2
Welcome to the forums.
Not sure what a dipole breaker is.
You can't randomly increase a breaker size.
The breaker amperage is dictated by the gauge of the wiring.
It sounds like that pump may be on a #14 gauge/15A circuit which means it may require you to run a new 20A circuit on #12 wiring.
Not sure what a dipole breaker is.
You can't randomly increase a breaker size.
The breaker amperage is dictated by the gauge of the wiring.
It sounds like that pump may be on a #14 gauge/15A circuit which means it may require you to run a new 20A circuit on #12 wiring.
#3
Member
Thread Starter
Join Date: Oct 2018
Location: USA
Posts: 4
Received 0 Votes
on
0 Posts
My mistake - meant a 2 pole breaker. Since I have no openings in the breaker box for a new one, what did you think of the 150 ft 12/3 run from the 30 amp breaker in my shop - currently nothing on it.
#4
For some unknown reason it was/is powered by a 15 amp dipole breaker along with several receptacles, light fixtures and outlets.
what did you think of the 150 ft 12/3 run from the 30 amp breaker in my shop - currently nothing on it.
You don't need 12/3 for 120V. What you need is 12/2.
All wiring on the circuit will have to be 12 AWG, so you will have to run a dedicated line to the pump instead of connecting to existing circuit.
#8
Member
Thread Starter
Join Date: Oct 2018
Location: USA
Posts: 4
Received 0 Votes
on
0 Posts
Hypothetical question. Could I have two 12/2 UF lines from my shop (150 ft) to the septic pump and float switch - one for each. If so, should I change the existing 30 amp breakers for 20's?
#11
For some unknown reason it was/is powered by a 15 amp dipole breaker along with several receptacles, light fixtures and outlets.
Where are these receptacles and lights? #14 wire on a 15 amp breaker was correct for the original 1/3 HP motor, but since you upgraded to a 1/2 HP motor the requirements have changed. If the lights and receptacles are near the source for the circuit you need to find them another circuit to be added to so that the motor circuit is dedicated to just the motor. Then, all you have to do is replace the 15 amp breaker with a 20 amp breaker. My motor data calculator calls for #14 wire on a 20 amp breaker for the 1/2 HP motor.