Adding 100 amp subpanel to garage.

I have 100 amp panel in my home and I want to add a 100 amp subpanel to my detached garage. I have 8 breaker slots open. What wire size do I need to get to power underground to my garage 60ft away?
 
  #2  
Old 10-21-18, 08:55 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,977
Received 194 Upvotes on 170 Posts
If you actually need 100 amps for the new panel i doubt your existing service is large enough. Is that the panel size of the load expected?
 
  #3  
Old 10-21-18, 09:03 AM
B
Member
Thread Starter
Join Date: Oct 2018
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
I don't have an expected load offhand. Only things I'd have to power are lighting , outlets and considering adding a mini split. It is a 3 car garage with a shop space attached and I might actually rent it out. That's probably not helpful.
 
  #4  
Old 10-21-18, 09:44 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,977
Received 194 Upvotes on 170 Posts
It would be most.helpful to know the expected load so the feeder can be sized appropriately. It is senseless.to move.forward.without good information.
 
  #5  
Old 10-21-18, 01:38 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,704
Received 273 Upvotes on 230 Posts
Just to answer the technical requirement, for 100A you need either #3Cu or #1Al with a #8Cu or #6Al ground.
 
 