Is it not advisable to branch off a dishwasher power line to another receptacle?

Is it not advisable to branch off a dishwasher power line to another receptacle?

Reply

  #1  
Old 11-16-18, 11:04 AM
Member
Thread Starter
Join Date: Jul 2010
Location: USA
Posts: 928
Received 0 Votes on 0 Posts
Is it not advisable to branch off a dishwasher power line to another receptacle?

I want to install an under sink hot water/filter tank; however, I have no receptacle to plug in or power the unit. I was wondering if I can just get power from dishwasher power line. Is it against code or highly not advisable?
 
Sponsored Links
  #2  
Old 11-16-18, 11:16 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
It depends on how many watts each appliance is rated for and how many amps is the circuit. It is unlikely you can share a circuit with an instant water dispenser because those usually require a full 15A by themselves.
 
  #3  
Old 11-16-18, 11:50 AM
Member
Thread Starter
Join Date: Jul 2010
Location: USA
Posts: 928
Received 0 Votes on 0 Posts
I see. So, as long there is enough wattage and amperage, it's fine, correct?
 
  #4  
Old 11-16-18, 12:26 PM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,457
Received 15 Votes on 15 Posts
My last home had code that prohibited sharing a DW circuit. Is this water heater supplying the DW?
 
  #5  
Old 11-16-18, 12:38 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The rules in the code are that if either appliance is more than 50% of the ampacity of the circuit, it requires a dedicated circuit; and both appliances together cannot exceed 80% of the circuit ampacity.

For a 15A circuit this means any appliance greater than 900W (7.5A) needs a dedicated circuit, and the two together cannot exceed 1500W (12A).

For a 20A circuit this means any appliance greater than 1200W (10A) needs a dedicated circuit, and the two together cannot exceed 1800W (16A).
 
  #6  
Old 11-16-18, 02:29 PM
Member
Thread Starter
Join Date: Jul 2010
Location: USA
Posts: 928
Received 0 Votes on 0 Posts
Awesome! Thanks for the explanation. Looks like I'll need a dedicated line or something else.

No, this water heater do not supply the water to the DW.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: