garage sub panel location

Hi, I am installing a sub panel in my garage. I've read conflicting rules about sub panel locations. I have 2 prefered locations for one in my garage. On Mike Holts site I saw a diagram stating 15" from the center line to each side needs to be obstruction free. Power wiil come in bottom of panel via 2" pvc conduit. Is there any convience related problems with these locations that I may be overlooking

First location is between the garage doors.

The other ( prefered) is on a 4' span wall. Entrance door is on the right side of panel. The door hinge is on the panel side the door could potentially swing in front of panel.

Are these location acceptable?
 
Attached Images   
Sponsored Links
  #2  
Old 11-17-18, 02:18 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Yiu need 30 inches side to side but it does not need to be centered. You must have 36" in front of the panel. Is this a detached garage?
 
  #3  
Old 11-17-18, 06:13 PM
Member
Thread Starter
Join Date: Jun 2001
Location: USA
Posts: 382
Received 0 Votes on 0 Posts
Yes detached garage. 30" side to side is total, correct? So if I put a 3 sided box around the panel it would be 30" wide x 36" deep, correct? Plenty of room in front. The entrance door doesn't matter?
 
  #4  
Old 11-17-18, 06:18 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,022
Received 68 Votes on 60 Posts
I would not put it between the garage doors. I would think the rails might be considered an obstruction. Where you have it to the left of the man door is a better place all around.
 
  #5  
Old 11-17-18, 08:11 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,980
Received 35 Votes on 30 Posts
I too go with the wall option. I too consider the rails to be in the workspace.

Mike Holts diagram should say 30 inches total, not centered on panel. The panel can be all the way at the edge of the 30 inches. The panel door needs to open at least 90 degrees.
 
  #6  
Old 11-18-18, 10:45 AM
Member
Thread Starter
Join Date: Jun 2001
Location: USA
Posts: 382
Received 0 Votes on 0 Posts
Thanks for the input. Next to the man door it is.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: