UF-B I just trenched to shed is missing the ground - Now what?

UF-B I just trenched to shed is missing the ground - Now what?

Reply

  #1  
Old 11-27-18, 06:35 AM
scoob8000's Avatar
Member
Thread Starter
Join Date: Apr 2005
Location: USA
Posts: 183
Received 0 Votes on 0 Posts
UF-B I just trenched to shed is missing the ground - Now what?

I just burried about 75 feet of 12/2 UF-B to my shed from the back of my garage. I didn't realize the ground was missing until I was done and started to open the cable up to connect it.

The package clearly says 12/2 with ground. I'm going to call Southwire and complain. But what now?

I really only planned on an outlet or two and a couple lights?

I guess I can run everything thru a GFCI in the shed. Or would I be better off pounding a ground rod at the shed?
 
Sponsored Links
  #2  
Old 11-27-18, 06:39 AM
Member
Join Date: Oct 2005
Location: USA
Posts: 1,439
Received 15 Votes on 15 Posts
That's a pretty major quality hit for Southwire. How far back in the jacket did you look?
A new ground rod will not fix this issue.
 
  #3  
Old 11-27-18, 07:03 AM
scoob8000's Avatar
Member
Thread Starter
Join Date: Apr 2005
Location: USA
Posts: 183
Received 0 Votes on 0 Posts
It's gone at both ends of what I put in, and my remaining cuttings. I thought at first it was just pulled out, but upon a closer look there isn't even a void in the jacket for it. I have some pics on my phone I'll try to upload here in a few.
 
  #4  
Old 11-27-18, 07:49 AM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,687
Received 30 Votes on 29 Posts
Expect the seller to take back the cable and give you full credit or refund even though the cable "has been installed and used and possibly cut." It is defective in manufacturing, labeling or packaging.

I do not think that there is any legitimate AC power use for that cable although it would make good speaker cable.
 
  #5  
Old 11-27-18, 08:12 AM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,228
Received 27 Votes on 22 Posts
Pictures will definitely be good. I wonder if they packaged landscape wire in wrong packaging?
 
  #6  
Old 11-27-18, 11:34 AM
scoob8000's Avatar
Member
Thread Starter
Join Date: Apr 2005
Location: USA
Posts: 183
Received 0 Votes on 0 Posts
Pics.. The jacket definitely looks like normal UF-B, inner conductors feel like normal #12 conductors..

Tried calling southwire twice but can't seem to get ahold of anybody knowledgeable. Filled out their web form for defective product.





 

Last edited by scoob8000; 11-27-18 at 11:56 AM.
  #7  
Old 11-27-18, 11:53 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,245
Received 482 Votes on 452 Posts
Wow..... that's a first. It's the wrong product in that package as they do manufacturer two and three wire UF without a ground.

SouthwireŽ copper UF-B cable is manufactured as a 2 or 3 conductor cable, with or without a ground wire. Copper conductors are annealed (soft) copper, solid or compressed stranded. Phase conductors are polyvinyl chloride (PVC) insulated, nylon jacketed, color coded for identification purposes. Jacketed with sunlight, moisture and fungus resistant gray PVC
 
  #8  
Old 11-27-18, 01:09 PM
scoob8000's Avatar
Member
Thread Starter
Join Date: Apr 2005
Location: USA
Posts: 183
Received 0 Votes on 0 Posts
Interesting. I couldn't find one without a ground. Wonder what the use is there?

So all this aside, all I really plan on using this for in the shed is a battery tender, and a couple lights.

What's the thoughts on just using plastic boxes and not worrying about it? I'll feed it thru a gfci for a little extra safety measure and slap the ungrounded outlet sticker on it.
 
  #9  
Old 11-27-18, 01:45 PM
Join Date: Jan 2009
Location: Trumbull, CT, USA
Posts: 419
Received 3 Votes on 3 Posts
I don't think there is much use for an un-grounded circuit today but I am not an electrician but I see no harm as long as there is nothing metal on the battery tender and use plastic boxes and those porcelain or a plastic keyless/pullchain fixture. I would GFCI protect the wire where it leaves the breaker panel
 
  #10  
Old 11-27-18, 07:32 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,239
Received 40 Votes on 32 Posts
Where did you buy that stuff?
 
  #11  
Old 11-27-18, 08:56 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,239
Received 40 Votes on 32 Posts
that's a first. It's the wrong product in that package as they do manufacturer two and three wire UF without a ground.

For what code compliant purpose would UF-B cable be manufactured without a ground?
 
  #12  
Old 11-27-18, 08:58 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,245
Received 482 Votes on 452 Posts
My only thought was low voltage lighting.
Maybe it's for those who like to pull it into metal conduit.
 
  #13  
Old 11-28-18, 06:00 AM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,687
Received 30 Votes on 29 Posts
Having been installed yesterday, it is not grandfathered as an old ungrounded circuit equippable with ground fault circuit interrupter. It will not pass code.
 
  #14  
Old 11-28-18, 09:39 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,239
Received 40 Votes on 32 Posts
My only thought was low voltage lighting.

It would certainly work, but there is 14-2 and 12-2 low voltage cable available that's a lot less expensive than 600 volt rated ungrounded UF-B cable. There must be a market for it if Southwire makes it.
 
  #15  
Old 11-29-18, 12:53 PM
Member
Join Date: May 2015
Posts: 432
Received 17 Votes on 10 Posts
Adding to the curiosity, this product listing from Southwire shows the UF-B without ground as only available in 12AWG, 2 or 3 conductor. So whatever market it's for, it's quite specific about the wire size.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: