Grounding a hot tub sub panel

i have a hot tub that is hooked up to a gcfi box that goes to a sub panel. I started getting mild shocks from it. I have been told it is a grounding issue so I went out and got a grounding rod, connector and 4 gauge wire. Now, should I ground the main box or the gcfi box? Also, if I ground the main box do I detach the old ground wire? The other problem is the ground wire I got is really thick and is not going to mount to either ground bar...

Any suggestions would be appreciated. I have photos of the boxes but was not sure how to put them in this post.
 

Last edited by HughG; 11-27-18 at 06:25 PM. Reason: Typos
Sponsored Links
  #2  
Old 11-27-18, 06:36 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,166
Received 475 Votes on 445 Posts
Welcome to the forums.

Is this a 120/240v hot tub ?
If yes...... you should be using four wires. Two hots, a neutral and an insulated ground.
If you are getting a shock.... something is not wired correctly.
You do not use a ground rod at the tub.

Please post pictures for us........ How-to-insert-pictures
 
  #3  
Old 11-27-18, 07:53 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,221
Received 38 Votes on 30 Posts
I'd like to see a picture of the spa panel with the GFCI breaker. It sounds as if the feeder neutral and feeder ground are both terminated on the neutral bus. I saw that one time on an inground pool many years ago (mid '70s) when only the pool light was required to be GFCI protected and a slight shock could be felt in the water when the light was turned on. Isolating the neutral from the grounded panel box solved the problem.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: