Power problem in bathroom

Reply

  #1  
Old 11-28-18, 12:39 PM
Member
Thread Starter
Join Date: Nov 2018
Posts: 3
Received 0 Votes on 0 Posts
Power problem in bathroom

I am having power problems in my bathroom. When I turned on the lights they flicker and go out. I also have no power at the wall outlets. I have replaced the ground fault outlet and the breaker. They all worked a few days ago.
 
Sponsored Links
  #2  
Old 11-28-18, 12:59 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,207
Received 477 Votes on 447 Posts
Welcome to the forums.

Is the problem circuit dedicated to the bathroom only or are there more devices in the house on it ?
 
  #3  
Old 11-28-18, 01:07 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
This problem is usually a burned off or loose wire in one of the junction boxes feeding this circuit. A burned crimp is a common cause as is a bad back-stab wire in a switch or receptacle. Finding it can be tricky since it could be at any junction box, receptacle box, switch box or light fixture on the circuit.

The fix is to open up each box, remake connections and replace devices if they are worn or loose, use screw terminals instead of back-stab push in connections.
 
  #4  
Old 11-28-18, 02:53 PM
Member
Thread Starter
Join Date: Nov 2018
Posts: 3
Received 0 Votes on 0 Posts
It's on a dedicated circuit, as I think about it, the closet light in the bathroom has not been working but began working just before evrytevery went dead. I think I will start with that fixture. First thing tomorrow, got to work right now.
 
  #5  
Old 11-30-18, 10:37 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,230
Received 39 Votes on 31 Posts
began working just before evrytevery went dead.

What's an evrytevery? .............
 
  #6  
Old 11-30-18, 02:40 PM
Member
Thread Starter
Join Date: Nov 2018
Posts: 3
Received 0 Votes on 0 Posts
Got it! Not what I expected. Turned out to be a bad outlet in the living room. I used a lamp to trace backwards to the last functional outlet on the same wall. When I opened it the damage was clear. I replaced the outlet and that solved the problem.
 
  #7  
Old 11-30-18, 03:05 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Good job. Thanks for letting us know the outcome.
 
  #8  
Old 12-01-18, 06:22 AM
Member
Join Date: Mar 2014
Posts: 481
Received 7 Votes on 7 Posts
What I would check would be the GFCI receptacle in the bathroom. Bathroom receptacles tend to get more of a work-out than other ones. GFCI receptacles have pressure plates that the conductor is inserted into an then the screw tightened down. It is possible that over time if the screw was not tightened very well that the conductor may not be making full contact with the pressure plate. The lighting may be being feed from the line side of the GFCI. Does the GFCI receptacle work properly?
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: