450' electrical line run
I want to supply 50 amps to my motorhome which is 450' from 150 amp service service panel. What size wire do I need to accomplish this?
#2
If you'll want to be running both A/C units you will need considerably larger sized wiring.
Are you looking for direct burial or are you running conduit ?
To stay under a 3% voltage drop you will need at least #1 copper or 2/0 aluminum.