Can I use a 2-wire with ground to run 220 Circuit?

First timer here...
I have a 110 circuit (30 amp) breaker at main box. It has a #10 2 wire w/ground that runs through the attic and out an exterior wall in a junction box. I would like to use this circuit to power a garage with get this a "220 circuit". This would include installing a distribution panel in the garage.
Can this be accomplished with #10 2 wire w/ground and adding a separate ground and ground rod next to the garage?.
I am assuming this wire was run when the house was built as there are two bulkhead walls that extend floor to roof (House was built to withstand category 4 hurricane) there is no attic access between the bulkheads. Installing new 3 wire w/ground conductor would be very expensive...
  • There is a 30 amp 110 breaker for this circuit
  • A couple of blank spaces in the main box to add 220 breaker
  • Total length of run Main to Distribution Panel about 130 feet
  • Want to run welder in garage that requires 220v 20 amp breaker
Thanks in advance for your expert advice...
JAMdozer...
 
Sponsored Links
  #2  
Old 11-30-18, 01:10 PM
Member
Join Date: Nov 2015
Posts: 1,282
Received 22 Votes on 20 Posts
If you use 240V only (it is 120V and 240V in the US and Canada), you can. Most welders are 240V only.
You just have to mark white wire with black , red, or blue electric tape to repurposed it as hot wire and connect white wire to one of the poles on the breaker.

Adding additional ground will make no difference because you cannot use ground wire as current carrying wire.
 
  #3  
Old 11-30-18, 01:21 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
But you will need to weld by the light of a coal oil lamp. Code says only one feed to a detached structure so if an existing 120v feed it would have to be abandoned.
 
  #4  
Old 11-30-18, 01:57 PM
Member
Join Date: Nov 2015
Posts: 1,282
Received 22 Votes on 20 Posts
The op said it is on 30A, so I assumed it is not the part of existing lighting or receptacles.
Also, I assumed it is attached garage.

If this in fact is detached, then you will have to run 8 AWG or 6 AWG then install a sub panel.
 
  #5  
Old 11-30-18, 03:11 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
I may have guessed wrong when I read:
  • Total length of run Main to Distribution Panel about 130 feet
 
  #6  
Old 11-30-18, 04:17 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,983
Received 35 Votes on 30 Posts
You cannot add a ground and a ground rod to allow that cable to also supply any 120 volt circuits.
 
  #7  
Old 12-01-18, 11:47 AM
Member
Thread Starter
Join Date: Nov 2018
Location: United States
Posts: 2
Received 0 Votes on 0 Posts
First off, thanks to all for your valued input...

Seems that I can use the existing conductor to run 240v circuit

But will not have 120v circuit because both black and white conductors would be hot...120v circuit would require a neutral???

I would definitely want to have lights and 120 outlets for power tools...

Thanks
JAMdozer
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: