Can I use a 2-wire with ground to run 220 Circuit?
First timer here...
I have a 110 circuit (30 amp) breaker at main box. It has a #10 2 wire w/ground that runs through the attic and out an exterior wall in a junction box. I would like to use this circuit to power a garage with get this a "220 circuit". This would include installing a distribution panel in the garage.
Can this be accomplished with #10 2 wire w/ground and adding a separate ground and ground rod next to the garage?.
I am assuming this wire was run when the house was built as there are two bulkhead walls that extend floor to roof (House was built to withstand category 4 hurricane) there is no attic access between the bulkheads. Installing new 3 wire w/ground conductor would be very expensive...
JAMdozer...
I have a 110 circuit (30 amp) breaker at main box. It has a #10 2 wire w/ground that runs through the attic and out an exterior wall in a junction box. I would like to use this circuit to power a garage with get this a "220 circuit". This would include installing a distribution panel in the garage.
Can this be accomplished with #10 2 wire w/ground and adding a separate ground and ground rod next to the garage?.
I am assuming this wire was run when the house was built as there are two bulkhead walls that extend floor to roof (House was built to withstand category 4 hurricane) there is no attic access between the bulkheads. Installing new 3 wire w/ground conductor would be very expensive...
- There is a 30 amp 110 breaker for this circuit
- A couple of blank spaces in the main box to add 220 breaker
- Total length of run Main to Distribution Panel about 130 feet
- Want to run welder in garage that requires 220v 20 amp breaker
JAMdozer...
#2
If you use 240V only (it is 120V and 240V in the US and Canada), you can. Most welders are 240V only.
You just have to mark white wire with black , red, or blue electric tape to repurposed it as hot wire and connect white wire to one of the poles on the breaker.
Adding additional ground will make no difference because you cannot use ground wire as current carrying wire.
You just have to mark white wire with black , red, or blue electric tape to repurposed it as hot wire and connect white wire to one of the poles on the breaker.
Adding additional ground will make no difference because you cannot use ground wire as current carrying wire.
#4
The op said it is on 30A, so I assumed it is not the part of existing lighting or receptacles.
Also, I assumed it is attached garage.
If this in fact is detached, then you will have to run 8 AWG or 6 AWG then install a sub panel.
Also, I assumed it is attached garage.
If this in fact is detached, then you will have to run 8 AWG or 6 AWG then install a sub panel.
#7
Member
Thread Starter
Join Date: Nov 2018
Location: United States
Posts: 2
Received 0 Votes
on
0 Posts
First off, thanks to all for your valued input...
Seems that I can use the existing conductor to run 240v circuit
But will not have 120v circuit because both black and white conductors would be hot...120v circuit would require a neutral???
I would definitely want to have lights and 120 outlets for power tools...
Thanks
JAMdozer
Seems that I can use the existing conductor to run 240v circuit
But will not have 120v circuit because both black and white conductors would be hot...120v circuit would require a neutral???
I would definitely want to have lights and 120 outlets for power tools...
Thanks
JAMdozer