I currently have 120v going to my garage with overhead wiring. It has one insulated and bare neutral. I want to run 240v to the garage. Am I able to run 2 insulated and bare neutral to a sub panel with itsi own ground?
 
Sponsored Links
  #2  
Old 12-06-18, 12:49 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
No. You can only have one power feed to a detached structure. You will need to abandon the current 120v feed and install a sub panel supplied by two hots, one neutral, one ground.
 
  #3  
Old 12-06-18, 01:07 PM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,551
Received 20 Votes on 20 Posts
The present setup is incorrect as it stands. You are not permitted to have a bare neutral or combined neutral/ground with the hot wire wrapped around it..

But you can add a second hot and an (insulated) neutral which together with the existing wires and all juxtaposed will give you the desired 120/240 volt feed assuming they are all fat enough for your expected electric load.

The first panel in the outbuilding (your proposed subpanel) needs both a ground wire (equipment grounding conductor) back to the feeding panel and ground rod(s) (normally two) just outside.
 
  #4  
Old 12-14-18, 08:15 AM
Member
Thread Starter
Join Date: Dec 2018
Posts: 4
Received 0 Votes on 0 Posts
So, I need 4 insulated and a messenger wire to support? How do I attach to the messenger? What wire designation do I need to use? I know the gauge depends on power needs.
 
  #5  
Old 12-14-18, 10:40 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
UF-b cable. Use sunlight resistant wire ties to hold to a messenger such as plastic coated 1/8' steel cable. The messenger must be grounded at one end.
 
  #6  
Old 12-14-18, 11:49 AM
Member
Thread Starter
Join Date: Dec 2018
Posts: 4
Received 0 Votes on 0 Posts
I'm used to running Romex and conduit, so this overhead stuff is new to me. If the messenger wire has to be grounded at one end, why can't it be grounded at both and serve as the ground? Thank you for all your help!
​​​​​​
 
  #7  
Old 12-14-18, 12:37 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
The steel cable isn't rated for electrical work but for safety needs to be grounded.
 
  #8  
Old 12-14-18, 02:33 PM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
The messenger cable would have to be ACSR electrical grade which is a mixture of steel and aluminum strands to use it as the ground. Plain steel makes a poor electrical conductor outside due to surface corrosion. A plain messenger wire is usually grounded through the attachment to the steel conduit mast.
 
  #9  
Old 12-14-18, 02:46 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Note since xx-3 UF-b contains a ground it is pretty much a moot point. If you use quad plex the messenger is rated for use as a ground,

As I recall you were running a 60 amp circuit. Finding #6 (#4 al) quad plex would be more difficult though you could of course go larger. I therefore just went with UF-b.
 
  #10  
Old 12-18-18, 09:57 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,050
Received 26 Votes on 20 Posts
A #8 aluminum quad is all that's necessary for 60 amps in free air, but it would be a special order. I'd just use the UF-B like Ray suggested.
 
  #11  
Old 12-21-18, 11:47 AM
Member
Thread Starter
Join Date: Dec 2018
Posts: 4
Received 0 Votes on 0 Posts
Where I live, it's all special order. When I went in the small town lumber yard, they didn't even know what ufb was. When they checked they couldn't even special order it for me. Thank y'all for your insight and know how.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: