60 amp disconnect with 70 amp circuit

Howdy,
Have #6 wire run to a detached garage wherein I will be installing an electric on demand hot water heater. The 13kw size calls for a 60 amp circuit and the 16kw size water heater calls for a 70 amp circuit...both using the #6 wire.

I am going to install a non-fused disconnect in front of the water heater, but my question is this: can I use the non-fused 60 amp disconnect if I elect to use the 16kw water heater that requires a 70 amp circuit?

The larger unit draws 66 amps.

Thanks!
 
Sponsored Links
  #2  
Old 12-20-18, 08:06 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
If there is already a 120 volt supply to the garage you can't run another power source. Sounds like you need to run a 100 amp subpanel to the garage if your main panel will even support it.
 
  #3  
Old 12-20-18, 08:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,114
Received 374 Votes on 351 Posts
A 16kw heater on #6 wiring is really pushing it.
You can use a disconnect larger than what the circuit is protected at but not smaller.
 
  #4  
Old 12-21-18, 05:53 PM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: USA
Posts: 10,042
Received 26 Votes on 20 Posts
can I use the non-fused 60 amp disconnect if I elect to use the 16kw water heater that requires a 70 amp circuit?

That would require a 100 amp disconnect.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: