Electrical inspection question

Easy question. I hae a 70' run of conduit in a 18" deep trench. Will the inspector want to see the entire run or can I start to bury it it. Leaving the ends and a few sections in the middle uncovered.

TIA
 
Sponsored Links
  #2  
Old 12-22-18, 12:46 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 54,185
Received 475 Votes on 445 Posts
There is absolutely no set answer.
With a homeowner installation..... I'd recommend leaving the entire trench open.
 
  #3  
Old 12-22-18, 03:27 PM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,219
Received 26 Votes on 21 Posts
As said, best to leave it open. Also NEC calls for 18" of cover, so that's from the top of the conduit, not from the bottom of the trench.
 
  #4  
Old 12-22-18, 03:46 PM
Member
Thread Starter
Join Date: Jun 2001
Location: USA
Posts: 382
Received 0 Votes on 0 Posts
Thanks for the replies
I'm actually down 24"
 