We had an inspection done on our house last week. The inspector stated under a concern for electrical that our main panel box is not bonded properly to the neural system. What does this mean exactly and is this something that we can fix ourselves?
 
Sponsored Links
  #2  
Old 05-25-01, 04:30 AM
Visiting Guest
Posts: n/a
well,
you probably need an MBJ, or main bonding jumper. this is usually a screw, or mettalic piece that joins the grounding and grounded ( or neutrals & bare grounds) together.

perhaps you could get the panel make & model, and chase thios down at an electrical supply house...
 
  #3  
Old 05-29-01, 10:15 AM
Member
Join Date: Sep 2000
Location: Fayetteville, NY, USA
Posts: 1,052
Received 1 Vote on 1 Post
If the "Main Panel" is the electrical enclosure housing the main disconnecting device for your electric service (Main Breaker), then the NEC requires the neutrals and grounds to be "bonded" together. In lay terms this means "connected". Wirenuts correctly explained this, but I'll add to it just a bit. Most new panels come with a "bonding screw", but it is often NOT installed because certain circumstances prohibit its use. But it is supposed to be installed in the main panel. There is a hole in your neutral bus, probably near where your main service entrance conductors are connected. This screw simply goes right through the neutral bus and taps into the steel of the enclosure, making the two a common point. Your neutral and ground bus bars are also screwed right to the steel of this enclosure. One screw seems simple enough, but in this case you will have live electrical feeders very close to where you would be working, and killing the main breaker will not de-energize these conductors. An experienced electrician would likely be able to do this in 2 minutes without disconnecting your house from the utility, which is the only way to cut the power in that enclosure.

Does that make sense?

Juice
 
  #4  
Old 05-29-01, 11:24 AM
Visiting Guest
Posts: n/a
Thumbs up o.k.

I kind of understand, Thanks for the reply. So basically it's not a significant problem that we should worry about, right?
 
  #5  
Old 05-29-01, 11:48 AM
Member
Join Date: Sep 2000
Location: United States
Posts: 18,497
Received 0 Votes on 0 Posts
Wrong!

The previous posts only say that the problem should be relatively simple to correct. They did not mean to imply that it's not an important problem. It is very important. The grounding system in your house (if you have one) is not functioning properly.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: