Kitchen Circuit 30 amp Breaker

When we built our house there was no electricity available so I started to wire the house for a 12 volt system. Before the 12 volt system was put to use electricity became available. I had run a single 8/3 ga cable to the kitchen area for the 12 volt system and that circuit now has a 20 amp breaker. Now many years later the microwave and our new Instant Pot can't be running at the same time. The wiring could certainly handle more amps and I have considered replacing the 20 amp breaker with a 30 amp breaker. Yes I know this is against code and I probably won't do it but is there any other alternative other than running a new circuit?
 
Sponsored Links
  #2  
Old 02-07-19, 10:59 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 56,451
Received 761 Votes on 715 Posts
Yes...... you could install a small sub panel at the end of the 8/3. Put a 2P40A in the main panel. Then you could take off several circuits.
 
  #3  
Old 02-07-19, 11:04 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,325
Received 190 Votes on 168 Posts
What Pjmax said or you could install a double pole 20 amp breaker and have two 20 amp circuits. Put the microwave and Instant Pot on separate 20 amp circuits.
 
  #4  
Old 02-07-19, 03:49 PM
F
Member
Thread Starter
Join Date: Dec 2009
Location: alaska
Posts: 4
Received 0 Votes on 0 Posts
I posted this topic and I made a stupid mistake in describing my situation. I am used to marine wiring and in that realm 12/2 is two conductors so I said I had 8/3 going to my kitchen when in reality it is two wires plus a ground. It took me a while to figure out what the two replies were talking about, it didn't make sense to me. Thank you for the replies though.
 
  #5  
Old 02-07-19, 05:06 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,325
Received 190 Votes on 168 Posts
In that case neither option suggested will work. You are face with pulling in new cables for new circuits.
 
  #6  
Old 02-07-19, 07:06 PM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 3,932
Received 52 Votes on 50 Posts
If the cable has two 8 gauge wires, black and white respectively, and a ground wire at least 10 gauge then you can still have a subpanel with multiple 20 amp. sub-subcircuits, either two or three of them.
 
  #7  
Old 02-07-19, 08:32 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
But it would be a 120v only breaker panel.
 
  #8  
Old 02-08-19, 06:24 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 3,932
Received 52 Votes on 50 Posts
Planning for the future you will need to run more cables.

Ultimately you need two 20 amp circuits serving kitchen and dining room receptacles only. The (120 volt only) subpanel accepting the existing 8-2 cable can power those two circuits only, or IMHO power one of the dining circuits and two 15 amp general purpose circuits with lights.

For the future new cables would power lights, other rooms, etc. and possibly one of the official kitchen 20 amp circuits.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: