Sub panel replacement

Hi I have a 70amp breaker running to a detached garage what size sub panel can I use? Thanks
 
Sponsored Links
  #2  
Old 02-24-19, 10:43 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,100
Received 372 Votes on 349 Posts
Welcome to the forums.

You can use a 100A panel. It will be protected by the 70A breaker. If it contain more than 6 breakers then it needs a main breaker in it. The sub panel will require a separately purchase ground block.

This is a basic panel from Depot. It's in their homeline series. Even comes with a ground bar.
homedepot/Square-D-Homeline-100-Amp-6-Space-Surface-Mount-Panel
 
  #3  
Old 02-24-19, 01:29 PM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,175
Received 23 Votes on 19 Posts
I highly suggest something at least this size with the main breaker.
https://www.homedepot.com/p/Square-D...00PC/204836383
 