14 Gauge Light on 20 amp circuit

So contractor is wrapping up a master bath remodel. I have been peaking in there and saw a seperate 14 g wire clearly labeled lights... i thought temp for power while remodeling.

walls are now closed, wrapping up etc and that 14 g is still connected to 4 led lights. Switch being fed by 12g wire.

I know LEDs draw pretty close to nothing but just wanted confirmation this is ok. 12g feeds the heat lamp in the ceiling. The LEDs would never draw even close to overheat 14g but they are connected....

thoughts?
 
Sponsored Links
  #2  
Old 02-25-19, 06:30 PM
Member
Join Date: Jun 2012
Location: USA
Posts: 1,411
Received 12 Votes on 11 Posts
It is wrong. What did the inspector say?
 
  #3  
Old 02-25-19, 06:41 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 14,903
Received 23 Votes on 19 Posts
Regardless of what the leds draw, unless the circuit is protected by a 15 amp breaker it is wrong.
 
  #4  
Old 02-25-19, 06:47 PM
Member
Thread Starter
Join Date: Jul 2008
Location: New York (Long Island)
Posts: 28
Received 0 Votes on 0 Posts
Yea i will check the breaker to see if 15 ir 20 amp. Maybe he used i.e. cause of the heat lamp to be safe and it's on 15 amps. I will check. Had a feeling it was wrong
 
  #5  
Old 02-26-19, 04:45 AM
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 20,760
Received 184 Votes on 171 Posts
The key is the breaker size. There is nothing technically wrong code wise with having 14ga wire in the circuit as long as it's 15 amp. Maybe the electrician didn't have enough 12ga on hand and used the 14ga he had. If it is a 20 amp circuit then all the wiring must be 12ga.
 
  #6  
Old 02-26-19, 08:46 AM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,499
Received 15 Votes on 15 Posts
You might have also run into a catch 22. After downgrading that circuit to 15 amps you might no longer have a 20 amp circuit for the bathroom.

It would satisfy code to add a 20 amp circuit with a home run to one new duplex receptacle in the bathroom.
 
  #7  
Old 03-01-19, 02:40 PM
Member
Thread Starter
Join Date: Jul 2008
Location: New York (Long Island)
Posts: 28
Received 0 Votes on 0 Posts
Thanks all, spoke to contractor who said it is the other way around, he has the power coming appropriately but uses the 12 g on the heat lamp just for extra protection
 
  #8  
Old 03-01-19, 06:04 PM
Member
Join Date: Nov 2015
Posts: 1,188
Received 15 Votes on 14 Posts
uses the 12 g on the heat lamp just for extra protection
Using 12 g doesn't make it any safer than using 14 g if the breaker is 15A.
Using larger gauge will help with voltage drop for a long run, but I doubt your run is that long.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: