14 Gauge Light on 20 amp circuit

Reply

  #1  
Old 02-25-19, 07:26 PM
I
Member
Thread Starter
Join Date: Jul 2008
Location: New York (Long Island)
Posts: 28
Received 0 Votes on 0 Posts
14 Gauge Light on 20 amp circuit

So contractor is wrapping up a master bath remodel. I have been peaking in there and saw a seperate 14 g wire clearly labeled lights... i thought temp for power while remodeling.

walls are now closed, wrapping up etc and that 14 g is still connected to 4 led lights. Switch being fed by 12g wire.

I know LEDs draw pretty close to nothing but just wanted confirmation this is ok. 12g feeds the heat lamp in the ceiling. The LEDs would never draw even close to overheat 14g but they are connected....

thoughts?
 
  #2  
Old 02-25-19, 07:30 PM
A
Member
Join Date: Jun 2012
Location: USA
Posts: 1,649
Received 48 Votes on 43 Posts
It is wrong. What did the inspector say?
 
  #3  
Old 02-25-19, 07:41 PM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 15,218
Received 103 Votes on 89 Posts
Regardless of what the leds draw, unless the circuit is protected by a 15 amp breaker it is wrong.
 
  #4  
Old 02-25-19, 07:47 PM
I
Member
Thread Starter
Join Date: Jul 2008
Location: New York (Long Island)
Posts: 28
Received 0 Votes on 0 Posts
Yea i will check the breaker to see if 15 ir 20 amp. Maybe he used i.e. cause of the heat lamp to be safe and it's on 15 amps. I will check. Had a feeling it was wrong
 
  #5  
Old 02-26-19, 05:45 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 24,426
Received 747 Votes on 686 Posts
The key is the breaker size. There is nothing technically wrong code wise with having 14ga wire in the circuit as long as it's 15 amp. Maybe the electrician didn't have enough 12ga on hand and used the 14ga he had. If it is a 20 amp circuit then all the wiring must be 12ga.
 
  #6  
Old 02-26-19, 09:46 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,283
Received 109 Votes on 101 Posts
You might have also run into a catch 22. After downgrading that circuit to 15 amps you might no longer have a 20 amp circuit for the bathroom.

It would satisfy code to add a 20 amp circuit with a home run to one new duplex receptacle in the bathroom.
 
  #7  
Old 03-01-19, 03:40 PM
I
Member
Thread Starter
Join Date: Jul 2008
Location: New York (Long Island)
Posts: 28
Received 0 Votes on 0 Posts
Thanks all, spoke to contractor who said it is the other way around, he has the power coming appropriately but uses the 12 g on the heat lamp just for extra protection
 
  #8  
Old 03-01-19, 07:04 PM
L
Member
Join Date: Nov 2015
Posts: 1,552
Received 92 Votes on 80 Posts
uses the 12 g on the heat lamp just for extra protection
Using 12 g doesn't make it any safer than using 14 g if the breaker is 15A.
Using larger gauge will help with voltage drop for a long run, but I doubt your run is that long.
 
 