100 amp disconnect

What size wire do I need to run from a 100 amp breaker to a 100 amp 3 phase disconnect 15 feet apart?
 
Sponsored Links
  #2  
Old 03-06-19, 10:29 AM
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,944
Received 42 Votes on 40 Posts
Assuming THHN in conduit, no smaller than #3 copper or #2 aluminum.
 
  #3  
Old 03-06-19, 10:30 AM
Member
Join Date: Mar 2010
Location: USA
Posts: 3,505
Received 17 Votes on 17 Posts
deleted ...........................
 
  #4  
Old 03-06-19, 11:40 AM
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,162
Received 23 Votes on 19 Posts
#1 Al is 100A, #2 Al is 90A.
 