Room wiring help needed. (I am a novice.... help)
This is the room i need wired but i dont know how to do this properly . The light 1 corresponds with switch 1 and so on .. i would prefer this all on 1 circuit if possible i have a feed wire from box at 10 awg on a 30 amp breaker all new .. breaker should maybe be reduced idk if 30 amp is to much but i know its rated wire for 30 amp

Last edited by PJmax; 03-19-19 at 08:46 PM. Reason: image
#2
First thing is you need to change the breaker to 15 or 20 amp. Lights and receptacles are not permitted on a 30 amp circuit.
I would just go around the room s2,s1, plug, plug, plug. Then sw1 to l1 and s2 to l2.
I would just go around the room s2,s1, plug, plug, plug. Then sw1 to l1 and s2 to l2.
#4
Member
Thread Starter
Join Date: Mar 2019
Location: usa
Posts: 3
Received 0 Votes
on
0 Posts
fair enough i agree with that on the breaker thing i knew 30 was to high. is 20 amp to high for celing lights? I have read that most plugs are ran 20 amp and most lighting is 15 depending on the specialty of the lighting of course. my question is now this. is it ok to run this all on 1 circuit the lighting is just plane light fixtures no fans ect. the plugs run just random small appl like vacumn,tv,dvd,and directtv box, with the exception 1 plug is a 110 or 120 whatever a/c window unit.. Also this house has walls not as thick as normal its old very old the plugs are mounted external not inside the walls so my question. Can i wirenut in the attic or do i need to run double down in a normal fashion and pigtail at the plugs?? this would be very unsightly of course but safety is my first..
#5
You want it all on one circuit with a small A/C. Then you must use #12 on a 20A breaker.
If you had two circuits then you could use smaller wire.
If you have shallow walls you are going to have problems. Typically only one cable is allowed in a shallow box. Maybe post a picture or two of the room for us. We need to know all the details to help you.
If you had two circuits then you could use smaller wire.
If you have shallow walls you are going to have problems. Typically only one cable is allowed in a shallow box. Maybe post a picture or two of the room for us. We need to know all the details to help you.
#6
Member
Thread Starter
Join Date: Mar 2019
Location: usa
Posts: 3
Received 0 Votes
on
0 Posts
lol no insulation , the walls are two 1 in boards shiplap this house was built in 1918 there are no recepticles in the walls they are all mounted on the outside with romex leading down the wall in plain site . well romex where the knob and tube has been replaced in a attempt to upgrade. some places the wiring is ran in the window trim where plugs are near windows.. # 12 is fine by me i had just ran a # 10 from my panel for a 110 hot water heater that turned out to be trash so i removed it . i hate to waste the wire i just ran i can change the breaker to 20 amp and use the existing 10 awg to run this 1 room ???? i was asking about the pigtail because i prefer to only have 1 ugly romex running per plug down my walls where everyone can see them
.. im guessing that would require juction boxes per wirenut set in the attic ?

#8
You will have even more.of an issue with box fill when using the larger wire and it will be a pain to work with.
If you run .metallic conduit you can cut down on box fill by using the conduit as the ground.
If you run .metallic conduit you can cut down on box fill by using the conduit as the ground.
#9
Hi, do you have a basement ,is it possible to install floor outlets ? That may eliminate some of the cables on the walls.
Depending on the size of the window AC you may want to consider a separate circuit for it.
Geo
Depending on the size of the window AC you may want to consider a separate circuit for it.
Geo