Plasma cutter
#1
Member
Thread Starter
Join Date: Mar 2008
Posts: 6
Received 0 Votes
on
0 Posts

I want this:
https://www.eastwood.com/eastwood-ve...hoCyNkQAvD_BwE
Someone kindly tell me what I need to say to my electrician so he can wire the source for this plasma cutter Want to cut 3/8" ....
https://www.eastwood.com/eastwood-ve...hoCyNkQAvD_BwE
Someone kindly tell me what I need to say to my electrician so he can wire the source for this plasma cutter Want to cut 3/8" ....

#2
From the manual. Tell this to your electrician.
Our Versa-Cut Plasma Cutter is supplied with the popular NEMA 50P plug, requiring a NEMA-50R recepticle. If a 220-240 VAC, 30 Amp outlet is used a UL listed 30 Amp plug may be installed by a licensed and qualified electrician
#3
Since the plasma cutter comes with a 50 amp plug I would have him install a 50 amp receptacle (NEMA 6-50R) using wire/cable rated for 50 amps. That way if you can use the same receptacle for a welder. The circuit breaker can also be a 50 amp two pole breaker.
#4
Scroll down to page 4 for installation requirements
:
https://www.eastwood.com/images/pdf/12740_versacut.pdf
:
https://www.eastwood.com/images/pdf/12740_versacut.pdf
#7
Strange that this unit will operate on a 20 amp 120 volt circuit, but needs a 30 amp circuit when running off 240 volts. I believe I'd wait on the circuit till I could see the data plate on the unit.