2014 NEC in effect. 210.52(E)(3) requires a receptacle accessible from the deck. I have three semi-related questions, trying to get a feel for the scope of the electrical work associated with a deck build. Any work required will be done by an electrician, but the amount of electrical work will influence how much budget can go to the deck itself.

Is there a general consensus on what "accessible" is? If I can reach an existing receptacle from the deck, it's accessible, but if I have to get off the deck, it's not? (I have an existing exterior receptacle about 2 feet from the deck location, no problem to run a cord to it through the railing, but I'd have to get off the deck to do it.)

Does the required receptacle have to be on its own circuit?

Can conduit (or an alternative like SE cable) be run from the existing outdoor receptacle, and onto the deck structure? For example, if I wanted a receptacle surface mounted on a railing post?

Thanks!
 
Sponsored Links
  #2  
Old 05-03-19, 07:38 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 53,567
Received 413 Votes on 387 Posts
(3) Balconies, Decks, and Porches. Balconies, decks, and porches that are attached to
the dwelling unit and are accessible from inside the dwelling unit shall have at least one
receptacle outlet accessible from the balcony, deck, or porch. The receptacle outlet shall
not be located more than 2.0 m (61∕2 ft) above the balcony, deck, or porch walking
surface.

On the wall next to the deck would not be accessible from the deck.
It does not need to be on its own circuit. It does need to be GFI protected.
An extension cord to the deck would not be acceptable.
Using UF or conduit to run to a receptacle should be ok.
 
  #3  
Old 05-03-19, 08:18 PM
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 6,873
Received 96 Votes on 88 Posts
In Canada it does need to be on its own circuit.
 
  #4  
Old 05-04-19, 05:57 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 12,973
Received 59 Votes on 52 Posts
I would be surprised that a city would require you to install a receptacle just because you build a deck. If the deck is being installed with the interior being finished, I would suspect the existing electrical would be grandfathered in.

Of course, updating to the newest code is always a good thing as having a receptacle on a new deck is handy.
 
  #5  
Old 05-04-19, 07:42 AM
Member
Thread Starter
Join Date: May 2015
Posts: 431
Received 17 Votes on 10 Posts
We tend to suffer here more than most from the whims of the inspector. People have asked an inspector "is this OK?," been told yes, and then been failed when a different inspector handled the final inspection.

Theoretically, since IRC doesn't make any mention of a receptacle, the building inspector shouldn't have grounds to fail the deck for not having one, and if no electrical work is done at all, it doesn't get an electrical permit, or an electrical inspection. But that's in theory.

Since the update from 2011 to 2014 NEC changed the requirement from "within the perimeter" of the deck to "accessible from" the deck, it seems like it's now along the lines of the age-old "where subject to damage" discussion. It sounds like it doesn't have to be within the perimeter, but where does it have to be? I was hoping maybe the NEC Handbook had some more guidance on it. Shoot, I have a friend, who, if the required receptacle is 6 1/2 feet above the deck, wouldn't be accessible for her without a step stool.

North Carolina issued an opinion stating: "The language in section 210.52(E)(1) of the 2014 NC Electrical Code has been altered from the 2011 edition mandating the required front and back outdoor receptacles from being 'accessible while standing at grade level' to being 'readily accessible from grade.' The new language allows for a receptacle to be located in the middle of the wall line of a deck that cannot be reach through the pickets so long as you can walkup the steps and access the receptacle without infringing on the 'readily' accessibility."

That's basically the reverse of what I'd need to do -- walk down the steps and use the 210.52(E)(1) receptacle to meet the deck receptacle requirement. Theoretically, if A=B, then B=A. But unfortunately that's North Carolina, not Maryland.
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: