Sub panel wire size questions.

I bought a house and the inspector tagged the wiring to the sub panel in the attached garage.

The main box (200 amp) is on the back of the house and conduit runs from a 50amp breaker from the there around the soffit and into the garage (about 30ft)

The wire used is THHN 8 AWG (two hot, two neutral, one ground.

Ive read that this is okay for 50amp service. Is that true?
 
  #2  
Old 05-07-19, 09:19 AM
A
Member
Join Date: Mar 2010
Location: USA
Posts: 4,298
Received 109 Votes on 101 Posts
The breaker in the main box used to feed this subpanel needs to be 40 amps or less for 8 gauge wire in cable or conduit. The breaker (if any) at the top of the subpanel can stay as-is.

If the conduit can get wet (like outside or buried) then the wire in it has to be water resisting, like THWN or THWN/THHN.
 
  #3  
Old 05-07-19, 09:22 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,943
Received 44 Votes on 42 Posts
Depends on the wiring method. If the #8 THHN is continuous through conduit it is acceptable at 50A. If it switches to a cable like NM or UF then it should be reduced to 40A. THHN in conduit has a higher temperature rating and therefore is rated for greater ampacity than cable assemblies.
 
  #4  
Old 05-07-19, 10:08 AM
E
Member
Join Date: Apr 2019
Location: USA
Posts: 126
Received 17 Votes on 16 Posts
Also, #8 is approved for a 50 amp breaker as long as this breaker and the panel it connects to are marked that they're rated for 75 deg C. Modern breakers and panels usually are 75 deg C rated, but older ones may not be. If unmarked, the 60 deg C wire ampacity must be used.
 
  #5  
Old 05-07-19, 01:15 PM
C
Member
Thread Starter
Join Date: May 2019
Posts: 4
Received 0 Votes on 0 Posts
Would I be able use 6/3 romex (in conduit) instead of the 8 awg THHN

 
  #6  
Old 05-07-19, 01:48 PM
S
Group Moderator
Join Date: Oct 2004
Location: WI/MN
Posts: 19,614
Received 98 Votes on 86 Posts
No, romex (nm-b) is not rated for outdoor use.

6 ga THWN is the answer.
 
  #7  
Old 05-07-19, 02:34 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,513
Received 125 Votes on 99 Posts
Was this a home inspector? Get him to tell you exactly why he tagged it.
 
  #8  
Old 05-07-19, 02:45 PM
C
Member
Thread Starter
Join Date: May 2019
Posts: 4
Received 0 Votes on 0 Posts
It was a hope inspector. He stated on the report that the breaker was oversized. 50amp breaker with 8awg.
 
  #9  
Old 05-08-19, 06:18 AM
A
Member
Join Date: Mar 2014
Posts: 572
Received 23 Votes on 22 Posts
If that is what he meant by "tagged" then change the breaker to a 40amp from a 50amp which will help (but that only solves half your issue). Again, if the conductors are THHN and not THWN you will still have an issue since the conductors are in conduit. Google the difference between the two.

Also you stated above that there are two hots, two neutrals, and a ground. Why two neutrals - or was that a typo?
 
  #10  
Old 05-08-19, 03:01 PM
C
Member
Thread Starter
Join Date: May 2019
Posts: 4
Received 0 Votes on 0 Posts
No typo, there’s 2 blacks (hots going to the supply), 2 whites (going to a buss bar on the left), and a green ground going to a bar on the right. I wish I know how to post a pic on here lol.
 
  #11  
Old 05-08-19, 03:37 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 33,582
Received 13 Votes on 11 Posts
I wish I know how to post a pic
How to Insert pictures ...........................................................
 
  #12  
Old 05-08-19, 05:45 PM
P
Member
Join Date: Feb 2016
Location: United States, Virginia
Posts: 1,513
Received 125 Votes on 99 Posts
If it's #8 THHN/THWN in conduit from panel to panel then as mentioned earlier a 50A breaker is okay as long as the devices(breakers) and panel connections are rated at 75 deg.C., if rated at only 60 deg.C then a 40A breaker is needed.
 
  #13  
Old 05-09-19, 06:55 AM
I
Forum Topic Moderator
Join Date: Feb 2005
Location: Near Lansing, Michigan
Posts: 10,943
Received 44 Votes on 42 Posts
You really don't have to do anything per code, but if all that's holding up the sale is a $10 breaker; change to 40A and never think about it again.
 
  #14  
Old 05-09-19, 09:41 AM
CasualJoe's Avatar
Member
Join Date: Jan 2010
Location: United States
Posts: 10,763
Received 97 Votes on 87 Posts
It was a hope inspector.

Assuming that is a typo and you meant "Home Inspector", I am not really too surprised. There are a few good independent home inspectors out there, but very few that know and are good at inspecting electrical systems.

I agree with ibpooks when he said:

You really don't have to do anything per code, but if all that's holding up the sale is a $10 breaker; change to 40A and never think about it again.
 
 